ive been having a dispute with another electrician about using 30A JB's on rings
a ring is made up of 2 legs of 2.5mm T+E,
2.5mm T+E ref method C has current carrying capacity of 27A
now surely the JB has to be rated higher than the cable, but using a 30A jb although this is less than the 32A MCB its only joining one half of the circuit and is still higher than the rating of the cable
the arguement is that he thinks i should be using 45A JB's as they are rated above the MCB
whats peoples feeling on this matter as this is the first electrician ive met in 10 years that ever had a problem joining a ring with 30A JB's
i also did a little reasearch and although i couldnt find the correct reference in the regs book wikipedia stated that the cable size in a ring should be rated at no less than 2/3 ( two thirds) of the MCB
meaning that the cable rating has to at least be 21.333A so a 30A jb would be sufficient by 8.66A
a also if 30A JB's were not sufficient why do wholesalers not stock a 32A jb?