Discuss 3amp in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Wilson12

-
Trainee
Reaction score
3
Will a 3amp fuse for a cooker hood extractor fan and lights wired in 1.5mm off a spur be okay.
There was no wattage for the fan and there was two lights.
Surely that can't draw more then 700 or so watts.
My boss complained why I did that,just checking he's not winding me up
 
Will a 3amp fuse for a cooker hood extractor fan and lights wired in 1.5mm off a spur be okay.
There was no wattage for the fan and there was two lights.
Surely that can't draw more then 700 or so watts.
My boss complained why I did that,just checking he's not winding me up
Can you not find out the Fan loading along with the loading of the lights? a simple clamp meter would help, you also have to think will the lights and fan be on at the same time, all of the time, I would say a 3A fuse would be OK, It's good to see you thinking for yourself Wilson, what exactly is your Boss saying to you, as a Trainee, he, your Boss ought to be taking the lead on any sort of questionable act on your part, anyway good luck.
 
fuse should be selected to protect the cable feeding the hood, irrespective of the actual load. but if the manufacturer stipulates a certain fuse rating, this should be taken into consideration.
 

Reply to 3amp in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
674
Good afternoon I hope everyone is keeping well. I have purchased a stainless steel recirculation cooker hood which has the double insulated...
Replies
3
Views
989
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello, I am renovating a house. I am rewiring myself. I am getting an electrician to install a new consumer unit & test all my work. I'm looking...
Replies
20
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
831

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock