The max disconnection time of a 30ma RCD is 300ms, which is 0.3 seconds, at x5 or 150ma the max disconnect is 40ms which is 0.04 seconds.
Those trip current / time values are intended to keep you in the AC-1 to AC-2 areas, so little risk of fibrillation, of the shock risk model:
The 0.4s standard for TN earthing, and the related 0.2s for TT earthing, follow similar arguments about keeping touch voltage (about U/2 for TN fault as R2 roughly like R1, more or less U for TT) and exposure time during the fault such that typical body resistance won't result in deadly current-time exposure. But that only sort of works for typical dry contact, hence in a bathroom the old (pre-RCD everything) standard for supplementary bonding to further reduce the local voltage differences during a fault.
 
So why does anything need to disconnect in 0.4s then? Life saving RCDs can trip up to 0.3s, thats only 1/10 slower.

Maybe 1/10 slower but at a vastly different fault current!
The RCD trips at 30mA in 0.3s, that fast enough to save most people from a fatal shock.
The 40A MCB trips at a current in the hundreds of amps in 0.4s

The 0.4s is to keep touch voltages down, prevent damage to cables from long durations of high current faults and that sort of thing.
 
Maybe 1/10 slower but at a vastly different fault current!
The RCD trips at 30mA in 0.3s, that fast enough to save most people from a fatal shock.
The 40A MCB trips at a current in the hundreds of amps in 0.4s

The 0.4s is to keep touch voltages down, prevent damage to cables from long durations of high current faults and that sort of thing.
That cant be right, the RCD "starts" to trip at 30mA but it depend what bit of the sinewave its at, in 300ms it could be peak voltage and current.

If you've ever had a shock from an RCD protected circuit you'll know it hurts just as much as non RCD, it just doesnt last as long.
 

Reply to 40A shower disconnection time in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi. I'm being tasked with installing an electric shower into a property that was built back in the 1980's. The main consumer unit has only 4 ways...
Replies
2
Views
1K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top