That's 300 milliseconds not 30.So why does anything need to disconnect in 0.4s then? Life saving RCDs can trip up to 0.3s, thats only 1/10 slower.
Discuss 40A shower disconnection time in the UK Electrical Forum area at ElectriciansForums.net
That's 300 milliseconds not 30.So why does anything need to disconnect in 0.4s then? Life saving RCDs can trip up to 0.3s, thats only 1/10 slower.
The max disconnection time of a 30ma RCD is 300ms, which is 0.3 seconds, at x5 or 150ma the max disconnect is 40ms which is 0.04 seconds.That's 300 milliseconds not 30.
oops! oscar'd. need me glasses on.The max disconnection time of a 30ma RCD is 300ms, which is 0.3 seconds, at x5 or 150ma the max disconnect is 40ms which is 0.04 seconds.
Those trip current / time values are intended to keep you in the AC-1 to AC-2 areas, so little risk of fibrillation, of the shock risk model:The max disconnection time of a 30ma RCD is 300ms, which is 0.3 seconds, at x5 or 150ma the max disconnect is 40ms which is 0.04 seconds.
So why does anything need to disconnect in 0.4s then? Life saving RCDs can trip up to 0.3s, thats only 1/10 slower.
That cant be right, the RCD "starts" to trip at 30mA but it depend what bit of the sinewave its at, in 300ms it could be peak voltage and current.Maybe 1/10 slower but at a vastly different fault current!
The RCD trips at 30mA in 0.3s, that fast enough to save most people from a fatal shock.
The 40A MCB trips at a current in the hundreds of amps in 0.4s
The 0.4s is to keep touch voltages down, prevent damage to cables from long durations of high current faults and that sort of thing.