Commercial scenario :
lets say 54m , mmm ok 16amp OCPD, mmm ok at 52m I think I will put a 20amp D/P isolator , humour me I will go on . Actually oh dear I've ran out of 4mm T/E , tell you what I will just use 2.5mm instead . Anybody see an issue , cable clear run on open spacious cable tray no influences just straight clear run .
I just know that someone will say it's fine cos 2.5mm will take 25 odd amps .
Conversations requested guys
 
Sorry guys not sure really what you mean . If I've broken some rules then I apologise . Oh and the cable size is after the isolator NOT A FUSED SPUR by the way
 
Lol , don't worry about it , some start posts like this as a wind up , but it has fallen out of favour in the last few days.
 
Oh don't worry about VD it's irrelevent ............ Isn't it . Let's see 2.5mm ooh about 40m max . 4mm what about 60 odd . Oh B type MCB BS60898 Schneider acti 9 10ka . Oh bugger lets just put the last few meters in 2.5mm
 
Hi Dillb . Well this is purely a scenario but I would have thought that the length if you were to carry on from isolator with 4mm then great but this wasn't the question . I've seen lots of installations where other sparks have ran circuit in X cable to an isolator then for some unbeknown reason dropped to cable Y . My question is why not run the whole lot in cable Y if it's ok to use this on the last few meters . I think not . What's your thoughts ?.....??????
 
I don't really understand what your point is? Your OP is about 4mm then isolator then 2.5 and now your on about 431.2.1 which is about having a neutral that's CSA is smaller than the line conductor.
 
Last edited:
Ok let's rephrase . If calculations show that cable x should be used then how is it ok to use cable Y for the last few metres of this run . I'm not arguing I'm just posing a question that's all . If cable Y could be used for last few metres of said circuit then why are we using cable x for the first bit ?
 
Ok let's rephrase . If calculations show that cable x should be used then how is it ok to use cable Y for the last few metres of this run . I'm not arguing I'm just posing a question that's all . If cable Y could be used for last few metres of said circuit then why are we using cable x for the first bit ?

Probably to meet max Zs figures and permitted volt drop
 
YOu work out your cable calcs on the length and CSA of the conductors used, so if the first 50 meters is 4mm then the final 4 meters is in 2.5mm then you calculate it accordingly.
 
Now your confusing me how can voltage drop be better on a smaller cable at the end of a circuit . Maybe understand if other way round
 
OK ignoring the 431.2.1 reference which appears irrelevant.

If you have a circuit that start in a large csa and then drops to a smaller csa then it is likely that the designer was ensuring that the volt drop limits for the circuit were not exceeded, however you have said that volt drop is immaterial in an earlier post.

Your description of a 54m circuit in 2.5/1.5 would exceed the 11.5 V limit, however if half the circuit were run in 4/1.5 then you may just make the limit.
 
totally agree that you calculate on length and current carrying capacity but if total circuit length equates to using 4mm where and how do you calculate using 2.5 without fusing down at point of isolation .
 
I said VD WAS irrelevent being pedantic of course it matters . .ok let's say the circuit is designed on the limit in 4mm , putting 2.5 at end would not be correct . Yes?
 
The whole circuit is suitable for 2.5/1.5 from a CCC consideration, so it is also suitable for 4/1.5 in terms of CCC.
therefore there is no need to fuse down.
The decreased resistance provided by the 4/1.5 serves to reduce the volt drop only.
 
Last edited:
The whole circuit is suitable for 2.5/1.5 from a CCC consideration, so it is also suitable for 4/1.5 in terms of CCC.
therefore there is no need to fuse down.
The decreased resistance provided by the 4/1.5 serves to reduce the volt drop only.
what do you abbreviate to CCC MATE
 

Reply to 431.2.1 again in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K
Hi all just here as an enthusiastic learner/diyer to gain knowledge and help on bits and bobs At the moment I am confused I have a new single...
Replies
20
Views
3K
I have a pressure washer that I got as part of "a good deal", actually an exceedingly good deal as I later found out. I've had it a while, I guess...
Replies
5
Views
1K
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock