Discuss 5.3 kw double oven on a 20 amp fuse with 2.5 cable in the Australia area at ElectriciansForums.net

Might be a stupid idea and I don't know the rating of the hob, but is there enough slack of the 6mm, to swap over to the cooker and vica versa...
I am still learning so please don't make me brew up:D

Hobs are normally rated higher than ovens, something in the order of 7kw
 
Diversity on a cooker works fine until Xmas day when they trip out. personally I think regs are out of date on this one. Take a 10 kW electric range cooker. 10kW/230V= 43 amps. 10 amps plus 30% remaining load (approx 9.9amps) =19.9 amps so 2.5mm twin and earth on a 20 amp, dont think so. "At the installers discretion" is a term we ought to use more. On top of that you`ve got an appliance that draws for long periods of time allowing heat to build up in the circuit. Its not like a kettle that runs for a couple of minutes at a time. 6 or 4mm on this OP specs every time for me,
 
Last edited:
Bung it on the 2.5 on a 20A breaker with 20A DP iso. You're happy, regs are satisifed and client doesn't feel shafted and may actually call you again. I really don't understand this attitude of 'charge the client for an unnecesary job just to punish them for changing their mind.' Repeat business is good no?
 
Last edited by a moderator:
Diversity on a cooker works fine until Xmas day when they trip out. personally I think regs are out of date on this one. Take a 10 kW electric range cooker. 10kW/230V= 43 amps. 10 amps plus 30% remaining load (approx 9.9amps) =19.9 amps so 2.5mm twin and earth on a 20 amp, dont think so. "At the installers discretion" is a term we ought to use more.
well on such a load then...yes....it would be up to the designer as to the right action to take here.....short of treating it as a commercial load...100% of the first load....80% of the second and 60% of remaining appliances....
 
well on such a load then...yes....it would be up to the designer as to the right action to take here.....short of treating it as a commercial load...100% of the first load....80% of the second and 60% of remaining appliances....

Well I was taught to build in redundancy and that diversity was to do with total demand not individual circuits but I may be wrong there.. May be considered old fashioned by some but Ive lost count of the times Ive come across burnt out 2.5mm on an oven. Whatever the regs say the buck stops with the installer, hoping the client doesnt cook much is daft in my book. I have always used 4 or 6 on an oven, might be over engineered in some peoples eyes but its a better quality job
 
diversity becomes a problem when people start adding all connected loads together and then applying diversity....doesn`t work as the overcurrent device and associated cabling will be woefully undersized/underrated.....but as has been said before....the "regs" as we see it...that is BS7671 and anything seconded to it.....OSG GN3 etc are but guidance notes after all and as such are open to question as regards issues like this.....of course it is wiser to go over rather than under in terms of protective devices and cable/s and theres the issue of futureproofing as well....but how far do you take it?....Diversity is there for us to utilise ...given the guidance laid out in BS7671....its just a case of how and where....like you wouldn`t apply diversity to such a thing as an instantainious water heater would you.....as someone who posted on this forum about 3 weeks ago was going to do.....until advised not to of course....
 
The diversity applies to a cooker incorporating oven, rings, grill and assumes that they won't all be drawing full power in one go. likelihood
is that a double oven will draw full current at some time. Better to upgrade cable accordingly.
 
Table A1 is concerning diversity on individual circuits and states 10amps + 30% of remainder. Table A2 is diversity of a whole system and states 10amps +30% Full load in excess of 10a
 
Last edited:
The diversity applies to a cooker incorporating oven, rings, grill and assumes that they won't all be drawing full power in one go. likelihood
is that a double oven will draw full current at some time. Better to upgrade cable accordingly.
yet again....looking at the appliance first...or if the appliance isn`t on site at the time of design....then gathering info (make model) etc from the client and doing a bit of research on it.....find out the KW rating etc...so as to calculate/design accordingly....isn`t that the difference between installers and electricians.......
 
Last edited:

Reply to 5.3 kw double oven on a 20 amp fuse with 2.5 cable in the Australia area at ElectriciansForums.net

Similar Threads

Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
844
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
Replies
10
Views
4K
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock