Discuss 5 core swa cable calcs in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi there , is there anything else to consider when using 5 core SWA instead of 4 core + separate Earth in three phase installations for cable calcs etc? Apologies but just moving in to the 21st century never used 5 core before
 
Not if you are using the 5th core as the CPC as it is not a live conductor.

Though you might want to question the need for it when the armour is almost always suitable for use as a CPC.
 
I must admit, I have found it great when putting in 16A 3phase sockets.
many of them come with threaded entry and not easy to use a banjo or an earth nut to get the cpc to the socket from the armour.

still use a swa gland on the socket end but don’t need to mess with connecting anything to it.
 

Reply to 5 core swa cable calcs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
896
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
482
I was the 2nd sparks taking over a garden office supply job. The first sparks had fitted 10 sq mm 3 core SWA, but it actually had brown, blue and...
Replies
5
Views
806
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
457
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock