Discuss 52 static caravans. what a HOOK UP in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
oh dear. BW glands sunbathing

20181220_142628.jpg
 
Static caravan? oh... you mean "Luxury Holiday Home"

I've dealt with Willerby/Victory/ABI in the past... they are very careful to never call their products "caravans" static or otherwise.

Is it a "caravan" on the blue flex on the right? No plug and socket combo?
And the next hole over? Just a hole... no cable... The spiders front door

The park I worked on had a new distribution box put in several years before I started. Each circuit was distinguished by a wrap of insulating tape around the SWA cable at the hook up point position. So you knew which box was on which circuit. No such thing as a circuit chart until I started there.
All fine until 10 years down the line when every piece of tape had either fallen off or became white through sunlight.
 
The time bomb here,is that the mains cable a 16mm 2 core swa,is using the outer galvanised steel as a earth,as they some do,not ideal,,but some firm used BW glands ip54.and as you see in the picture ,it's corroding,at the moment I'm collaiting info to get them back,,,ive informed the residents who own dogs not to let them near the hook ups, and keep them near the trees ,if they need a wee,,,IP,BANG
 
unless you can prove it is TNS it should be a TT supply and using the armour cpc just to protect the cable so 16mm is good, most places only have 10mm supplying multiple outlets.
bad idea if the glands are BW and corroded, esp if they are as bad at the supply end of the 16mm.
 
My site was 4mm swa to maybe 5 or 6 hook ups in a ring formation. Using a 3rd core for earth.
Place was extended and partial rewrite of old site as above a couple of years before I started.

Big local firm did it, but got the colours wrong. Ie, black for N, grey with earth sleeve brown for L
They were also connecting the vans with 1.5mm artic flex, not 2.5 as advised by the manufacturers. And some that had extras such as a washing machine or dishwasher were overloading the 16A mcb..... The old electrician they had was upping the breaker to a 20 without upgrading the flex size.
It was never the factory fitted appliances causing a problem... always the multitude of plug in heaters the owners brought in.
 
Foreigners were housed in 10 caravans in the fields where they work,16.00 mm 3 core supplying these.Amperage got up to 112 amps,melted the DB,re fused with 63 amp fuse,to protect the cable.
It’s now supplied by another 16 mm Swa,split 5 +5,so far so good,& it’s getting colder.
 
My site was 4mm swa to maybe 5 or 6 hook ups in a ring formation. Using a 3rd core for earth.
Place was extended and partial rewrite of old site as above a couple of years before I started.

Big local firm did it, but got the colours wrong. Ie, black for N, grey with earth sleeve brown for L
They were also connecting the vans with 1.5mm artic flex, not 2.5 as advised by the manufacturers. And some that had extras such as a washing machine or dishwasher were overloading the 16A mcb..... The old electrician they had was upping the breaker to a 20 without upgrading the flex size.
It was never the factory fitted appliances causing a problem... always the multitude of plug in heaters the owners brought in.
And are tenants still alive
 

Reply to 52 static caravans. what a HOOK UP in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
860
Had a call from a local caravan site… under new ownership, and creating some new pitches. Went to site to have a chat, the guy already knew I’ve...
Replies
9
Views
2K
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
I have a small caravan park with 8 pitches. Each have a Rolec Electrical Hook-Up unit fitted with a Rolec 16A Single Pole and Neutral 2 Module C...
Replies
14
Views
2K
Hi I wanted to run my car air con on a hook up at a camp site. Could I buy a mains hook up kit and run a charger to my vehicle battery. Would that...
Replies
1
Views
876

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock