Customer has himself fitted a new hob of 6.4kw in place of previous gas hob with electric ring x 1 ?
Under the hob there was x 2 sfcu both on there own circuits and both run in 1 x 2.5mm t/e.
He has connected his hob to one of the sfcu fused at 13a and on a 16a MCB at the board.

Using diversity this should do.
However, could he connect both runs of 2.5mm (in theory then 5mm) to a new cooker connection plate and place on 32a mcb covering the max 26.7a of the Hob.
Or is that a No No.
 
as long as the 2 cables are of equal length ( resistance) and follow the same route, then it's parallel conductors and should be OK. however, a 6mm cable with a cooker isolator and dual outlet pl,ate would be more conventional.
 
Somebody asked this same question a few weeks ago, but for installing a shower rather than a cooker. Might be worth searching for it, as there were many replies.
 

Reply to 6.4kw hob circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Evening all, I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the...
Replies
6
Views
2K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
758
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock