Discuss 6mm Earth and Main protective bonding conductors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

So my equation looks like this;

I=230/0.22(Ze) = 1,045
I2=1,045*1,045 = 1,092,025
I2*0.1 (t) = 109,202
Square Rooted = 330
330/143 (70 thermoplastic not bunched) = 2.3

So I only need 2.3 mm earth, something must be wrong?
 
Ian1981, sorry read and forgot your first post, got tied up with bedtime.......

I don't get how you get your 2300 amps, my Ze is 0.22, what calculation do I need to do?

Yes it's 60A, but how do I calculate fuse disconnect time?

I don't have the red version. Just checked latest version, it says replaced by BS 88-3
So I'm now on the right table, but don't know how to read it?

This is ridiculous!

You don't know how to calculate current, you don't know how to establish fuse disconnection times, you can't read the table once you've found it.
Seriously, stop attempting to do electrical work and hire a competent electrician.
 
Back to #1, I don't think you can ever prove the main protective bonding was adequate at the time and hence that it can be considered safe for continued use. The 15th Edition 1981 never gave a minimum size for main equipotential bonds if PME was employed just that you should consult the supply company, without digging out the book that is from memory so I stand to be corrected.
 
So my equation looks like this;

I=230/0.22(Ze) = 1,045
I2=1,045*1,045 = 1,092,025
I2*0.1 (t) = 109,202
Square Rooted = 330
330/143 (70 thermoplastic not bunched) = 2.3

So I only need 2.3 mm earth, something must be wrong?

Why must something be wrong? I haven't checked the figures but that is within the ballpark of what you would normally expect for a small supply like this.
 
Just seems so small when new installations require 16mm

Instead of blindly following a book try actually thinking about what determines the size and what the conductor is required to do.

It is not required to carry the current for any appreciable length of time, it only has to carry it for maybe one tenth of a second.
To take a very simplistic view look at a piece of 60A fuse wire, as long as your earthing conductor is bigger than that it will do its job.
 

Reply to 6mm Earth and Main protective bonding conductors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
709
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
776
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock