Discuss 6mm for 9.5 shower?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

c.boy

-
Reaction score
0
Got a shower to wire the length of the run is about 4m to d/p switch would i get away with 6mm ???yeah a would norm run a 10mm but this is for a friend who is struggling wi ££££!!and i have a load of 6mm!!! the shower is a 9.5 kw

thanks
 
Last edited:
You can get away with 6mm if the cable is clipped direct or is in free air. Though i always prefer wiring larger showers in 10mm.
4m is his given length but cant believe this is the full circuit length so how can you work this out without a realistic length he only gave the length to a dp switch and im assuming the shower aint in the meter cupboard.:eek:
 
Was only going by the cable size calculator that someone posted earlier and i put in a total length of 16m and it still gave me a result of 6mm try it. As i said 10mm is best.
 
Problem with the cable calc online is its too basic and dosnt take other factors into account its fine if your clipping in free air but we dont know enough to recommend this answer it will all change if the cable goes through loft insulation for example these minor details but significant points make the difference between good installation and an unsafe one. It would be better for c.boy to give us more detail before suggesting an answer as he will probably take the advice as good.
Sorry Pennywise not meant to sound like im having a go at you but applies to all who comment as this (lad) will take what advice is given and maybe be misdirected.
 
No offense taken, i do understand people can take things very literally if it suits them and can be misdirected with information that doesn't directly relate to their situation. In most cases it is probably easier to give less choices on solutions and always advise for the worst case scenario. cheers
 
As i thought!!! the shower is already bought, few month back!!!and the shop aint changing it!!a did say buy a 8kw but fell on deaf ears!!! so be it,they will have to get me some 10mm then.thanks to all!!!
 
fitted a 9.5kw shower instructions said it should be fitted on 40A breaker
so did this and it kept trippin

manufacturer said they are changing their booklet to advise 45A breaker

6mm cable can only carry 42 amps

so anything above 8.5 kw fit a 10 mm cable
 

Reply to 6mm for 9.5 shower?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt...
Replies
27
Views
1K
hi ive got an unused isolator in my airing cupboard that use to run a shower. no longer have has have combi boiler feeding a new shower. the...
Replies
16
Views
1K
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
634
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
Hi, I've got a customer who wants a 10.5 kW shower installed in his bathroom. As it happens he already has two unused 4mm T&E cables run from the...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock