I am completing a 9.87kWp install using 42 235W modules and a PowerOne 10.0-OUTD 3phase inverter, the PowerOne design tool recommended 2 strings of 21 modules however the string voltage is 826v and I cannot seem to find a DC isolator capable of greater than 800v.

Any recommendations or advise would be much appreciated?
 
Why not come off the panels as 4 strings, then use MC4 combiners to put them into 2 strings (by connecting in parallel). That will reduce your voltage to 413v and double your current
 
true "SNAP ACTION" 1000V DC isolators are not that common, I can only think of two true 1000V DC Isolator brands in the UK - this is one of them - I have seen the spec sheets for many brands that claim to be suitable for DC application, most (even big well known names) are not suitable for DC application at 1000V 16A but have still been installed all over the country... I have often wondered how many of the AC isolators that were used for DC application during the PV installation boom will need to be replaced and weather some one will have to die before this issue is addressed...
 
Most small enclosure true DC isolators are max 800v at 16 amps may be worth going 600v at 32amps and change config of panels.

but this is an old post and probably flogged to death.
 
Completely agree with your sentiment but, with all due respect, that Europa unit has a benedikt contact block inside it, as do the IMO units. Excellent products both because of that fact alone. 1000vdc ratings at the full contact current rating (16, 25 & 32A) is achievable by using the linking bars as per the tech specs although you do then "lose" a pair of poles in the 4-pole version. Santon have an equally high quality design, although they do offer a 4-pole switch that can disconnect 2 strings at 1000vdc (16 or 25A) each.

Some, inferior, "multi-pole" switches struggle to achieve 650vdc ratings even after series linking poles together....

As for how many "false" DC disconnectors are out there already, thousands upon thousands....but then I'm guilty of banging a drum about this for some time (although I do accept that it is a complex subject that has to be looked at from more than one angle)
 

Reply to 826v DC Isolator?? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

We don't normally do PV, however I was called to a PV inverter with no power, 6 years old Found supply OK, however fed through a AC type RCD. PV...
Replies
4
Views
765
At work we've got an 8 panel single string set up, going into a 3000w inverter via a double pole DC isolator. The AC goes supply > isolator >...
Replies
11
Views
3K
Hi everyone We have a little problem with a heating system on one of the projects (quite big house in south Kensington) and we are looking for...
Replies
14
Views
2K
Hi guys, I am new to the forum so be nice! I used to install solar PV systems back when the tariffs were still good, and I've never had to go...
Replies
5
Views
5K
I have 16 245w (declared capacity 3.84kW) panels on a south facing unshaded roof on the south coast of England producing around 4200 kW-h a year...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock