Discuss 9.5kw shower on a 6mm in the Australia area at ElectriciansForums.net

E

egginyourface

This has probably been done to death, but...

What is the best thing to do if you find 9.5kw shower on a 6mm cable and 40 amp breaker??

I told the customer cabling needs upgrading
 
how is thye cable installed. if it's clipped direct, part chased in masonry, no problem if not smothered in insulation.
 
Theres now way of telling installation method.

One thing that did worry me and suggested that original installer was a bit of a cowboy was that the earth cable had been snipped back in shower unit..

So i doubt any cable calcs had been done on this one
 
Nothing. Unless...

the circuit is over 39m long (would need to be a large house)
or
the installation method is not clipped direct or equivalent.

On what basis have you advised an increase to 10mm csa?
 
On the basis that the cable leaves the fusebox then disappears into a cieling making its way to 2nd floor bathroom. And the snipping off of the cpc tells me this was not installed by a competent person

Theres is no way of really knowing wether its covered in insulation or not...
 
The old shower packed up and plumber was called to replace it like for like. Its been working on 40amp breaker for a few years with no trouble. I did a insulation resistance test and it didnt show any break down in the cable...

What about insulation in the walls that the cable might be passing through??

Should i start cutting out holes
 
Im sorry if this is a bit of a daft thread... But don't really knw what shoudl be done in this situation.

The board looks like its been recently upgraded and the previous sparks seems to have thought a 40 amp breaker would be just fine.

Now i've been there and helped replace shower and it becomes my responsibilty
 
Ok, did as you suggested. Walls are full of insulation. Advised customer that cable be upgraded or shower can be downgraded.... Hes not very happy

thansk all
 
i've had similar happen to me. When i gave the customer the 'good' news, they thought i was at it, and bumped me off the job. Really don't understand why some 'sparks' even bother taking the risk. For the sake of litterally a couple of quid extra for bigger cable, which the customer would be paying for anyway, why risk lives?? Unless it was a plumber that thought he could upgrade the shower on his own...(also seen this)
 

Reply to 9.5kw shower on a 6mm in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I`m looking for an advice. I have an electric shower that I`m not using due to boiler changed to combi and added shower over bath feed by a...
Replies
1
Views
933
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
454
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock