Discuss A new smart meter is tripping RCD for 7 hours every night & I have a theory in the UK Electrical Forum area at ElectriciansForums.net

fearny26

DIY
Reaction score
7
Hi guys I have this problem that I've been trying to figure out all week.

On friday I had a 5 tail economy 7 smart meter installed and every night at 2 am the RCD trips and you cant reset it until 9 am so the problem is obviously to do with the off peak supply coming on. Theres only 1 rcd for the whole circuit (i know, its an old setup) and 2 wylex fuseboards for on peak and off peak.

Now i was sure it had to be a problem with the meter setup because Ive never had faults before and I had the RCD tested on monday and thats fine. The energy company say its a problem at my end so I checked the EICR from 2018 and i saw that they didnt check the off peak board because i guess they were there in the day. So I figure maybe theres a fault on the off peak board then but why has it only shown up now? The board has been on but ive never used the storage heaters so its usually switched off at the board although I've never used any of the circuits I assumed the board functioned as the RCD had never tripped.

So, when they replaced the electric meter they also removed these old heating contactors that switched on the off peak supply and now all the meter tails come directly from the meter to the henley block and then to the RCD and fuseboards.

So my theory is that in fact both the off peak board and the heating contactor switch were faulty and so the off peak board was never live and thus the fault not detected, but with the new meter and the contactor removed the off peak board is receiving power for the first time and the fault is now present and trips the RCD for the 7 hours each night.

For reference the on peak board supplies everything in the flat bar the storage heater which I have never actually used.

There is nothing in the property switching on at that time and the off peak board is in fact switched off at the breaker, I've also tried unplugging and switching every isolator but the fault remains so I believe the faulty board could still be capable of tripping the RCD

I moved to the flat 11 months ago and had no problems previously whatsoever

I am sorry if its not explained well this is my first property and I am learning about all this for the first time and I'm just looking for some help because I'm having no power each night for a week now and the energy company cannot/will not help so any answers on here Im grateful for

I've attached a photo of the two wylex fuseboards and the RCD and henley block. Also are the old and new meters, my meter is top right with 2 tails going straight in and 2 feeding the old heating contactor that I think was broken in the bottom right

Thanks
Jake
 

Attachments

  • 20191212_192048.jpg
    89.3 KB · Views: 105
  • 20200221_171135.jpg
    173.5 KB · Views: 102
  • IMG_20200826_170720641.jpg
    199.1 KB · Views: 113
Any forum members down that way? I bet one of our experts could find the fault it in 10 minutes.

the eicr should have picked up faults on both boards. It’s mainly a dead test and visual inspection. The fact that the off peak board was off shouldn’t have stopped them.

is it tripping with the off peak mainswitch off?
 
Unfortunately it’s nothing to do with the supplier/DNO as the fault is on your equipment.

It’s hard to see from your photos. What have you been provided meter wise? Do you still have 2 seperate, or are both tariffs supplied from one? do both boards share one neutral from the new meter? Does the RCD provide additional protection for both consumer units or just the main CU?

My money would be on Some sort of neutral issue, possibly neutral has been split after the RCD. Looks like one has been terminated in a Henley next to the meter. I’d check where the neutral from the meter runs for a start and if/where it splits.
but without decent knowledge and an MFT it will be very hard to diagnose.
 
Any forum members down that way? I bet one of our experts could find the fault it in 10 minutes.

the eicr should have picked up faults on both boards. It’s mainly a dead test and visual inspection. The fact that the off peak board was off shouldn’t have stopped them.

is it tripping with the off peak mainswitch off?

I've got a spark coming tomorrow hopefully to try disconnecting the off peak board see if that stops the trip

The only reason I wasn't sure about the EICR is because in the testing page it notes "off peak supply unable to live test" for the tests 1 to 3

Yes the off peak board is switched off when the RCD trips. I cannot reset the RCD for the 7 hour period each night which is why I think it has to linked to the off peak meter supply, could there be a bad meter tail perhaps and not the board?
[automerge]1598633758[/automerge]
Unfortunately it’s nothing to do with the supplier/DNO as the fault is on your equipment.

It’s hard to see from your photos. What have you been provided meter wise? Do you still have 2 seperate, or are both tariffs supplied from one? do both boards share one neutral from the new meter? Does the RCD provide additional protection for both consumer units or just the main CU?

My money would be on Some sort of neutral issue, possibly neutral has been split after the RCD. Looks like one has been terminated in a Henley next to the meter. I’d check where the neutral from the meter runs for a start and if/where it splits.
but without decent knowledge and an MFT it will be very hard to diagnose.


My meter is middle of the photo is 5 port dual tariff meter and both on and off peak supply come directly from the meter. There is the 2 incoming tails live/netural entering from the left (blue/brown) followed by 3 tails( 2 live and one shared neutral) entering the henley block in my ennclosure.

From the henley block I'm sorry I can't say for sure if the RCD covers both boards I don't know how to tell which cables which on a henley block I can tell you that each wylex fuseboard has a live and neutral cable and the RCD has one live and neutral.

Previously the meter had the on peak CU return neutral and the heating contactor had the return neutral for the off peak CU now it seems to share the one tail directly to the meter

It looks as you say that now there is only one neutral returning to the meter and the other is terminated into a new henley block installed with the meter. Could this be the issue

Again apologies if I am explaining this bad I am a long,long way from being any kind of electrician
 
Last edited:
was a thread recently where the suspect is the smart meter transmitting and tripping the RCD. shielding with foil seems to have cured it.
 
was a thread recently where the suspect is the smart meter transmitting and tripping the RCD. shielding with foil seems to have cured it.


Sorry I forgot to add on wednesday they sent out an engineer who just took the smart meter out and replaced it with a dumb meter but the fault remains so it must be something to do with changing from having the seperate heating contactor to the off peak being fed direct from the meter but I also saw what you're talking about to
 
As the others have said the fault will be on your side of the meter, and is probably:
  1. An N-E fault that has only become apparent with the change in supply having altered the usually-small N-E voltage enough to cause a trip-level current to flow, or;
  2. The off-peak board is now being energised (but before was not) and so tripping things.
It might be a fault that the original EICR did not pick up on, or it might be something more recent that has failed but did not manifest until the meter change (quite typical of N-E faults, they are usually a pain to find in the majority of cases with only 1 or 2 RCD that share several circuits).
 
As the others have said the fault will be on your side of the meter, and is probably:
  1. An N-E fault that has only become apparent with the change in supply having altered the usually-small N-E voltage enough to cause a trip-level current to flow, or;
  2. The off-peak board is now being energised (but before was not) and so tripping things.
It might be a fault that the original EICR did not pick up on, or it might be something more recent that has failed but did not manifest until the meter change (quite typical of N-E faults, they are usually a pain to find in the majority of cases with only 1 or 2 RCD that share several circuits).

If the off peak board is switched off at the breaker can it still trip the RCD?

I have experimented and switching the off peak board on and off during the 7 hour period when the RCD cannot be reset and it doesnt change the situation the fault remains whether the board is on or off, its only when i switch off the on peak CU that I can reset the RCD and when I switch the on peak CU back on it immediately trips. The on peak CU runs everything except storage heater which is unused.

I also tried unplugging everything and turning off all appliances at the isolator cooker/shower etc, I've found that with everything off and unplugged it will reset but the moment I turn any plug or appliance or light or any circuit on it trips the RCD.

This however does not happen outside of the 7 hour period and has certainly never happened before the meter exchange so whatever is changing on the circuit has to do with the off peak supply going live.

Do you think the difference in current tripping the RCD is because there is now a shared neutral when there wasn't before perhaps?
 
By the looks of it the one of the Neutral tails that originally went to the one of the Boards, is parked in the Henley type block below the meter to the bottom of picture 3.
That would mean one of the boards doesn't have a Neutral or both have been linled in the Henley to the right of the top Board
 
The fact the economy 7 CU had its own neutral but now is shared with the main CU would be where I’d look first. Where is the neutral supplied from in relation to the RCD? More than likely it’ll be a really easy fix. A N-E fault would probably trip whether the board had a live feed or not. Ie, not just at off peak times.
Hopefully you get it sorted tomorrow, and as has been said I’d be interested to hear what the fault was. Whatever happens though, could possibly be time at looking at an upgrade for those CUs ;)
 
Last edited:
Edit to above,
It looks like that parked tail was a Live which was switched by a now removed contactor for the Off peak and it's origin was in somewhere in the Henlys by the Consumer units
 
The fact the economy 7 CU had its own neutral but now is shared with the main CU would be where I’d look first. Where is the neutral supplied from in relation to the RCD? More than likely it’ll be a really easy fix. A N-E fault would probably trip whether the board had a live feed or not. Ie, not just at off peak times.
Hopefully you get it sorted tomorrow, and as has been said I’d be interested to hear what the fault was. Whatever happens though, could possibly be time at looking at an upgrade for those CUs ;)

Yes an upgrade would be ideal but the cost right now is less preferable ha.

Okay apologies for messy CU so setup is as follows

Of the four meter tails 2 enter the RCD at the top, one enters the middle back of the Henley and one enters the E7 CU directly.

Henley block is set out from left to right as follows
1 & 2 on the left are both tails From On peak CU
3 (rear middle) is meter tail
4 (front middle) goes to E7 CU
5 & 6 on the right enter the bottom of the RCD

On the meter side of things previously two tails came from the meter and two tails came from a seperate heat contactor now 3 tails come direct from the meter and one tail has been parked in a Henley block

Thanks guys for the replies so far

IMG_20200828_192014229.jpg
 
Maybe I’m confused.
If the off peak board only supplies storage heaters, and you don’t use them, turn off the OP board if the rcd holds like that until spark has a look.

it could be a fault on any of the heater circuits, never mind on the tails.
 
Maybe I’m confused.
If the off peak board only supplies storage heaters, and you don’t use them, turn off the OP board if the rcd holds like that until spark has a look.

it could be a fault on any of the heater circuits, never mind on the tails.

Yes the OP board is kept switched off but off or on the fault remains
 
The whole setup looks a bit disturbingly complex, and there seems to be more than one meter-set?

Hopefully the spark who visits can do a bit more systematic testing than we can guess from the photos.
 
Got it.

The Live to the Off Peak Consumer unit was sourced via the RCD.
Now it isn't.
But the Neutral still is.

There must be a small L to N leakage in the Off Peak C.U, enough to off balance the RCD.
And it will be on the Live side of the Main Switch
 
Got it.

The Live to the Off Peak Consumer unit was sourced via the RCD.
Now it isn't.
But the Neutral still is.

There must be a small L to N leakage in the Off Peak C.U, enough to off balance the RCD.
And it will be on the Live side of the Main Switch

Thanks so much for taking the time
Great work ill mention it to the spark when he comes over. I assume it would just mean replacing the fuse board then.


I'm really keen to use this as a learning exercise for myself I think I understand you're explanation but would you mind at all going over why this problem didn't happen before the meter exchange and what it is that's changed to bring about this problem. Sorry if its obvious
 
"Theres only 1 rcd for the whole circuit (i know, its an old setup) and 2 wylex fuseboards for on peak and off peak."
Source URL: A new smart meter is tripping RCD for 7 hours every night & I have a theory - https://www.electriciansforums.net/threads/a-new-smart-meter-is-tripping-rcd-for-7-hours-every-night-i-have-a-theory.189919/

Unless I'm being thick and missing something already covered, how can you have a single RCD covering two lines of supply?! In order for that to be it would have to be upstream of the meter, which it never would be unless the meter fitter had been smoking something herbal at the time.
 
Unless I'm being thick and missing something already covered, how can you have a single RCD covering two lines of supply?! In order for that to be it would have to be upstream of the meter, which it never would be unless the meter fitter had been smoking something herbal at the time.

On the original setup the meter only had a Single L & N out to the C.Us
This went direct to the RCD, through it then to the Henley where it split.
1 L & N supply to the Main C.U
Another Live went out to the contactor by the meter and came back in off the switched side to the Off peak Consumer unit.
The L to the Off peak now comes from the meter and misses the RCD, but the Neutral doesn't
 
Last edited:
"Theres only 1 rcd for the whole circuit (i know, its an old setup) and 2 wylex fuseboards for on peak and off peak."
Source URL: A new smart meter is tripping RCD for 7 hours every night & I have a theory - https://www.electriciansforums.net/threads/a-new-smart-meter-is-tripping-rcd-for-7-hours-every-night-i-have-a-theory.189919/

Unless I'm being thick and missing something already covered, how can you have a single RCD covering two lines of supply?! In order for that to be it would have to be upstream of the meter, which it never would be unless the meter fitter had been smoking something herbal at the time.

Yeah I wasn't sure if it covered both boards or not as my knowledge is limited.
Is it possible to do so by using the henley block or is it the case that the RCD just covers the on peak fuse board?
[automerge]1598697623[/automerge]
On the original setup the meter only had a Single L & N out to the C.Us
This went direct to the RCD, through it then to the Henley where it split.
1 L & N supply to the Main C.U
Another Live went out to the contactor by the meter and came back in off the switched side to the Off peak Consumer unit.
The L to the Off peak now comes from the meter and misses the RCD, but the Neutral doesn't


Yeah I think I get it, basically with the new meter tails configuration it has circumvented the RCD so that when the off peak board energises the rcd only gets half the picture and trips. Do you think this means my equipment is not faulty and I just need to have the RCD reconfigured on the circuit to work with the new arrangement then
 
Last edited:
this looks like a borrowed neutral or one connected to the wrong board.
you need someone who is experienced at fault finding.
 
Gotcha. That's proper muppetry!

On the original setup the meter only had a Single L & N out to the C.Us
This went direct to the RCD, through it then to the Henley where it split.
1 L & N supply to the Main C.U
Another Live went out to the contactor by the meter and came back in off the switched side to the Off peak Consumer unit.
The L to the Off peak now comes from the meter and misses the RCD, but the Neutral doesn't
 
Gotcha. That's proper muppetry!

If the meter and cutout were next to the Consumer units it would be fairly easy to see the problem.
I was immediately suspicious when I saw the Tail parked in a Henley at the meter.
At first I thought the meter person may have picked the wrong one off the contactor and was feeding a non RCD live onto the already live Henly near the C.Us
 
Hi guys I finally got some sparks out from the company that carried out my previous EICR and to confirm yes some proper muppetry had been carried out by the meter man. Below is the report they gave me hope it makes sense

Attended site as requested by customer
He explained to the RCD trips when the economy 7 kicks in
Carried out relevant test and found that the main switch RCD (TT) had been double fed and feeding back to off peak, this is a very dangerous situation due to the fact that when isolated it has 200 volts due to only the neutral been switch off and risk of electrocution
Also found economy 7 board wasn't even connect and left in 100a Henry block - disconnect the off peak supply wrongly install by smart meter installer and put back the correct cable for the off peak.
All tests passed the required standard to BS 7671.


My understanding was that he had fed the tails wrong into the henley block tbh I think he probably didn't even bother to check. The sparkies didn't take long to figure it out as the consumer unit is only the other side of the meter cupboard so visually is easy to see and all they had to do was re jig the tails and remove one and hey presto everything's fixed! They also tested all circuitry and everything was golden which was ace.

Now my next move is to go back to the supplier with the ombudsman's support and kick some arse hopefully but most importantly get them to pay for the invoice

Thanks everyone on here for the helpful responses
 
Result.

I don’t want to be disparaging about meter installers, but I think if there’s “only 4 cables” 2 in, 2 out.... then they got it easy.

add in a second board, off peak, and a time clock/ teleswitch and they are completely lost.
 
Dont agree with the comment about the neutral. We have loads of THTC or economy 7 stuff up here and the neutrals are marshalled together in a Henley block.

If the RCD can’t be reset for 7 hours The issue has to surely be connected to the off peak supply in some way if that is switching on/off at these times?
 
Dont agree with the comment about the neutral. We have loads of THTC or economy 7 stuff up here and the neutrals are marshalled together in a Henley block.

If the RCD can’t be reset for 7 hours The issue has to surely be connected to the off peak supply in some way if that is switching on/off at these times?
I’m sure the neutral has to be capable of being isolated via isolator which doesn’t interfere with normal supply which provides disconnection solely of the off peak other than affecting the on peak supply I had similar issue couple of years ago when installing a lot of storage heaters on a nationwide contract experienced so many different types of supplies
 

Reply to A new smart meter is tripping RCD for 7 hours every night & I have a theory in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day readers, if any,I am an old sparky, a very old sparky. I can remember old Faraday giving us lectures Wednesday evenings at evening...
Replies
1
Views
439
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
487
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
619
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock