Discuss Adding a dual appliance outlet plate to cooker circuit in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
1
Hi,

I want to add a 32a induction hob and 13a oven to my cooker circuit. I was going to make the current single outlet dual and then upgrade the MCB from 32a to 45a.

See photos of current setup.

Does this sound doable?

Thanks

Phil
 

Attachments

  • F14484AF-2AEF-478B-B2B3-F1D5DE115C15.jpeg
    336.6 KB · Views: 14
  • 96C51A66-1CF0-402C-A6E8-687F41A29953.jpeg
    188.5 KB · Views: 15
  • DABC8A5E-C5F3-474C-9CBC-F5C9BDBAF917.jpeg
    301 KB · Views: 18
  • 7E07272E-C906-4038-BCF1-7DEE0DF8A56F.jpeg
    492.9 KB · Views: 18
Is the circuit suitable to be upgraded to 45A (cable type, length, installation method, insulation etc.) ?
 
I thought those Memera 2000 ALB MCB's only came in 40A and 50A (assuming you could find one!), which might have a bearing on the adequacy of the cable in situ.
Others will know better than I, and what might fit!!
Might be safer to leave existing cable as is and use for the hob alone, and run an additional radial for the oven?
 
It is hard to see, but the existing cable into the outlet in the photo doesn't look likely to be rated at 45A.

In any case, do you actually need 45A, that is probably only a worst case current if you switched everything on max at the same time? In practice the maximum is likely to be a lot lower.
 
It is hard to see, but the existing cable into the outlet in the photo doesn't look likely to be rated at 45A.

In any case, do you actually need 45A, that is probably only a worst case current if you switched everything on max at the same time? In practice the maximum is likely to be a lot lower.

I have just been looking at the specs of the induction hob and oven. The hob has a max power output of 7kw and the oven is 2.3kw so a potential max of 9.3kw but in reality it would never reach that.

Do you think the 32a breaker would be sufficient for this?
 
I thought those Memera 2000 ALB MCB's only came in 40A and 50A (assuming you could find one!), which might have a bearing on the adequacy of the cable in situ.
Others will know better than I, and what might fit!!
Might be safer to leave existing cable as is and use for the hob alone, and run an additional radial for the oven?
Could you run a radial off the cooker circuit or would it have to come from the kitchen ring?
 
If you were treat the hob and oven as a single cooking appliance and apply the guidance on allowances for diversity (meaning we can rely on the probability that not all the hot plates are on all the time as well as the oven, and each element will be cycling on and off on their thermostats), then we get the following:

Diversity for a cooking appliance is the first 10 amps, then 30% of the remainder, plus 5 amps if there's a socket on the cooker switch.
This works out at 32 + 13 = 45 amps total before applying diversity.
So 10 amps plus 30% of 35 amps plus 5 amps. Which amounts to 25.5 amps.
Therefore you are within the maximum of 32 amps allowed by your current circuit.
 
If you were treat the hob and oven as a single cooking appliance and apply the guidance on allowances for diversity (meaning we can rely on the probability that not all the hot plates are on all the time as well as the oven, and each element will be cycling on and off on their thermostats), then we get the following:

Diversity for a cooking appliance is the first 10 amps, then 30% of the remainder, plus 5 amps if there's a socket on the cooker switch.
This works out at 32 + 13 = 45 amps total before applying diversity.
So 10 amps plus 30% of 35 amps plus 5 amps. Which amounts to 25.5 amps.
Therefore you are within the maximum of 32 amps allowed by your current circuit.
Thank you, that tells me everything I need to know 👍🏼
 

Reply to Adding a dual appliance outlet plate to cooker circuit in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello everyone, I've got a new oven and have a question about installing it. It's a 2.6kW 13A oven, and a cable from the 32A cooker circuit to...
Replies
2
Views
204
Hi All, I'm looking at installing an induction hob in my kitchen (upgrade from gas) and I gather that it can be added to the cooker circuit if...
Replies
1
Views
645
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
226
Cooker circuit has B40 MCB in the CU for the cooker, confirmed wired to the cooker outlet throughout, via a cooker switch & socket with a 10mm...
Replies
7
Views
1K
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock