Discuss Cooker circuit with new appliance not matching in the DIY Electrical Advice area at ElectriciansForums.net

Smasher

DIY
Reaction score
0
Cooker circuit has B40 MCB in the CU for the cooker, confirmed wired to the cooker outlet throughout, via a cooker switch & socket with a 10mm cable.

Issue is new cooker has a 1.5mm cable (fitted by manufacturer see image). It is 3.22KW rated load, and 16A fuse rating. The cooker connection too small to fit 10mm cable to.
Hob is gas but attached plug for ignition.

How to deal with this in a safe and sensible way? thanks.IMG_7046.jpeg
 
Last edited by a moderator:
Fused spur or plug and socket?
 
Fused spur or plug and socket?
I did consider the fused spur from the 10mm cable, but I’m not sure we can get the 10mm into one end of a spur. It’s probably the easiest of answers with that circuit in place, but I don’t know what the professional electricians would say about that. As much as it pains me, I’m considering putting a new MCB, say 32A, in a spare slot on the CU, a 4mm cable across to similar area and find a way from there, perhaps on another’s cooker switch. I find it bazaar that a new cooker is run on effectively what looks like a thin kettle lead.
 
3.22kW by 230v is exactly 14A, well within the design of 1.5mm cable.

How is the cooker connected? To a regular cooker outlet plate that already exists? Just connect the 1.5 to the 10 there, and downgrade the circuit breaker to 16A.
You won’t need to change the wiring in any way.

If the cooker comes with a cable attached, you’re not supposed to change it…

A cooker is classed as a fixed load…. It won’t be able to pull any more than the 3.22kW stated.
 
3.22kW by 230v is exactly 14A, well within the design of 1.5mm cable.

How is the cooker connected? To a regular cooker outlet plate that already exists? Just connect the 1.5 to the 10 there, and downgrade the circuit breaker to 16A.
You won’t need to change the wiring in any way.

If the cooker comes with a cable attached, you’re not supposed to change it…

A cooker is classed as a fixed load…. It won’t be able to pull any more than the 3.22kW stated.
Yes that sounds like a good solution. But just thinking about the plug socket on the cooker switch do I need to have a higher circuit breaker to accommodate that socket?
 
Don't see a problem with the 32A MCB, as far as the 1.5mm2 cable is concerned. It's a fixed load, so overload protection is not required, and in the event of a live to earth short circuit, it's no different to a short circuit live to earth on a spur off of a ring, where the 1.5mm2 cpc carries the full fault current.
Whether the oven manufacturer requires 16A fusing for the actual appliance is a different matter.
 
3.22kW by 230v is exactly 14A, well within the design of 1.5mm cable.

How is the cooker connected? To a regular cooker outlet plate that already exists? Just connect the 1.5 to the 10 there, and downgrade the circuit breaker to 16A.
You won’t need to change the wiring in any way.

If the cooker comes with a cable attached, you’re not supposed to change it…

A cooker is classed as a fixed load…. It won’t be able to pull any more than the 3.22kW stated.
Okay guys worked perfectly on a 16A fuse until I pushed it to the limit heat wise AND plug the kettle in to test. That tripped the 16A MCB
 

Reply to Cooker circuit with new appliance not matching in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
743
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
793
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...
Replies
1
Views
2K
I am reviewing a EICR for a property I am buying. The vendor has had the EICR done, but both the Cooker and Shower are on 40A 60898 B curve mcbs...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock