Discuss Adding RCD to existing Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
73
Was adding an RCD to a consumer unit so that both sides are protected, basically I’ve took the 2 lives from the load side of the main switch to the tops of the Rcds, then there’s a neutral going from the load side of the main switch to the first neutral bar I’ve doubled up a neutral there and took it to the top of the new (one closest to main switch) rcd. Then out other end I’ve took a neutral to the first neutral bar. Also from the first neutral bar I’ve took one to the top of the 2nd Rcd and then out the other side I’ve took it to the 2nd neutral bar. I’m getting 230v between live and neutral right through the new rcd but it won’t trip when I press the test button and also isn’t tripping when I’m doing RCD test on it. Am I doing something daft when connecting that up??
 
1615924686183.png

that how its done, example .
 
Last edited:
Are the neutrals on both sides of the 1st RCD connected to the same neutral bar? They shouldn't be.
Short answer - do what you have done with the live from the main switch with the neutrals, and each RCD has its own neutral bar on the load side.
For each RCD, the load neutrals need to be independent for it to see an imbalance.
 

Reply to Adding RCD to existing Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
378
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
2K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
I’ve had a disagreement with one of the Engineers in work. So we are doing an install. Installing an Intruder Alarm. Rather than go with my...
Replies
48
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock