Discuss adding socket like this in the UK Electrical Forum area at ElectriciansForums.net

Depends where you intend to put the crimp joints, not my way of doing it but it seems to be the norm these days,
 
You appear to have drawn a ring on a ring which is not OK.
You could add a socket as a spur from one of the sockets on the ring.
You could break the ring by removing the cable between two sockets and reconnect it through the new socket.
You also appear to be showing a crimp connecting three cables which is not good either.

View attachment 35425
 
You appear to have drawn a ring on a ring which is not OK.
You could add a socket as a spur from one of the sockets on the ring.
You could break the ring by removing the cable between two sockets and reconnect it through the new socket.
You also appear to be showing a crimp connecting three cables which is not good either.

View attachment 35425
I think the drawing is just poor, to me it actually only shows 1 leg of a ring being crimped, at first I thought it was as you describe, but I believe it is only 2 legs being crimped together, if it is the case, the drawing would have made more sense with the legs coming together in a ring shape!
 
It appears he has successfully added a socket using pencil and paper
Whether he is able to "practically" install this extra socket,it will take more on the job suggestions of method by the op to get his pass mark
 
On your last drawing,you have a ring showing the added socket having one leg connected to an existing socket
The other leg is crimped(in the wall) to what I assume will be a existing cable that was too short to reach the new socket
Question
If you are able to get cable to an existing socket,why do you not make the break in that socket and extend from there with your new cables?
If you do the job the way you suggest,what protection will be given to the buried joint you intend to make. how will you reinstate the insulation that will be removed ?
 
the socket i wish to move is in a silly place(right between a radiator and the door) im not sure on the protection i should have on the joints
 
the socket i wish to move is in a silly place(right between a radiator and the door) im not sure on the protection i should have on the joints

Ok ,there is misunderstanding for me in this thread
I was under the impression you were adding a socket to an existing ring

If you making a joint to extend elsewhere, a usual simple solution would be to crimp the cables in the box and use a blank plate (Be aware you need to maintain the feature of the cable being in a safe zone )

If its in a wall with no indication of the routing,you may need a different solution regards the cable protection
 
1 would leave the socket in place (the socket terminals are rather useful for joining the cables!) and add the extra socket...
 

Reply to adding socket like this in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Have a 63A RCD 5 Way box, with a 45A MCB, feds by 16mm2 tails, this in then feeding into a isolator via 10mm2 T&E, that then supplies the feed to...
Replies
8
Views
373
  • Locked
People with 10+ posts should not now see Google ads? Please reply and let me know what you can see? (This is Google ads, not the sponsors - who...
Replies
52
Views
3K
Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
852
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
208
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
819

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock