bit stuck on this job got a consumer unit (in a barn) fed from a house (tns) 3 phase mcb 63 amp the zs at the barn is 0.76 but after adding a rod and making it TT managed to get zs down to 0.5. ive got to add fire alarm panel and another sub board. there will be 100ma rcd before the consumer unit but the bit im stuck at is should the fire alarm feed also be before the 100ma rcd and what about the sub sub board, its 25m away from the sub board in 16 mm armoured.... would the best thing to do to add 300ma main rcd off that add 100ma to both the sub boards then 30 ma from there ? any advice appreciated

just to be clear it goes like this..... house tns with main board> barn sub board fed from house (also fire alarm going in same place ) > sub sub board fed from sub board
 
Disconnected the tns earth and just added the rod. The zs was 0.6 sorry not 0.5... I've left it as tns at the moment on a 40a mcb until I get my head round what to do with the fire alarm and sub board. Just had a thought though. The sub sub board I could split off 1 100ma rcd with the sub board but still stuck with the fire alarm should it go before or after the 100ma rcd ?
 
ok so heres what ive got,,,,,, ze in house is 0.47,,, sub board zs is 0.73,,, sub sub board is 0.82

house mcb needs to be at least 63 amp mcb to feed the sub board in the barn,,,barn sub board mcb needs to be at least 50 to then feed the sub sub board.....the customer is really objective to having a rcd inside the house incase it trips. any body see an option for me here ?
 
Couple of questions.
What is the purpose of this outbuilding isit a leisure building, why does it need a fire alarm?
Are there any extraneous conductive parts?
What size/core swa is feeding the outbuilding?



going to be a shop
no extraneous conductive parts all plastic
its all 16mm but upgrading will be as bad as getting a new main in. so customer said no to upgrade
 

Reply to Adding sub board to main consumer unit on tt in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
823
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
761
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
494
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock