Currently reading:
Adiabatic calculation confirmation

Discuss Adiabatic calculation confirmation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

DanBrown

Could anyone just confirm my results for adiquate earthing size and calculation using the adiabatic equation...

My test was on a ring main circuit wired in 2.5/1.5 pvc..
My supply voltage is 247v
My Impedance is 0.38 ohms.
The circuit is supplied via a RCBO 32a C type

My results suggest that a min CSA earth is 1.78mm2 and my cable CPC is only 1.5mm2.

Could someone just do a quick confimation of my answer please...
Is it a problem as such or not?? (still learning testing)
 
assuming the rcbo is going to operate in 10ms then i get the minimum CPC size of 0.57mm2 dont have big red book with me to cross reference breaker trip times. Fault Current = 247/0.38=650A so Sa = the Square root of (650 squared X 0.01) then divided by 115 = 0.565 edit. just checked my design calcs books type C 32A minimum cpc size of 1.5 so it should be fine.
 
Last edited by a moderator:
Firstly I am unsure why an adiabatic calculation is required. Is the floor area covered above 100m2 ?

The voltage used must always be 230v , all the equations in BS7671 are based on this voltage. also voltages will fluctuate dependent on demand etc...

need a bit more details, I deal more with design and understand why I would need to use the adiabatic equation, but I do not see why you are using it here.

perhaps I am missing something???
 

Reply to Adiabatic calculation confirmation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock