Came accross a remedial whilst at work where a previous engineer had raised a job to investigate poss borrowed neutrals on a lighting db which sits next to a general power db both fed from same rising busbar with same tap off supply characteristics i decided to isolate each individual circuit whilst clamped on the neutrals and check for any current to prove correct for corresponding curcuit however i came accross a situation where ever circuit was dead however one neutral was displaying around an amp on it but one disconnected from neutral bar to check any stray voltage cable was dead would i be correct in persuming poss phantom current due to over circuits and routing of singles fed from other db causing the clamp meter to pick this up ?
 
Is the circuit to which that neutral belongs RCD protected? If not, I suspect a neutral-earth fault. This can cause currents to circulate through neutrals with very little voltage driving them, hence the lack of significant reading when you disconnected it from the bar. Had it been borrowed by a circuit from a different DB that was still live, it would have floated up to line voltage (unless the load was switched off part-way through your test).

IR test to earth would be my next move.
 

Reply to Advice needed on neutral issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi all. Reasonably competant non electrical engineer homeowner here. I have a question for the experts: I recently replaced a horrible...
Replies
8
Views
1K
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
530
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
422

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock