Posting a message to the forum will remove the above advertisement

  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.
  2. Electrical 2 Go - Electrical Supplier and Electrical Wholesalers

    Please visit our prime electrical forum sponsor - they have the best tools at the best prices. If you find a price better somewhere else, call them or contact them, and they may be able to beat it for you. Especially on an order of a few items.

    Dismiss Notice

Discuss Advice on Installation in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Thomas Connolly
    Offline

    Thomas Connolly Regular EF Member

    Location:
    Kent
    Hi Folks,

    If I'm extending a lighting circuit, (adding two pendants and an outside light) from an existing pendant but the board doesn't have any protection (an old BS3036 fuse board) What's the best way to add RCD protection?

    The new cable for the switches can't buried more tore than 50mm deep and I don't want to whack an RCD FCU anywhere as they are quite bulky.

    What would be the best course of action to take to install this circuit so it complies with the Regs?

    Thanks,
    T
     
  2. SparkyChick
    Offline

    SparkyChick Making a banana smoothy for my fave gorilla Staff Member Moderator

    Location:
    South Wales
    Business Name:
    SparkyChick
    RCD FCU at the origin? Standalone RCD in an enclosure at the origin?
     
    • Agree Agree x 2
    • Like Like x 1
  3. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    Install an RCD in an enclosure next to the fuse board.
    Feed the RCD from the lighting circuit fuse and then feed the lighting circuit from the RCD.
     
    • Agree Agree x 5
    • Like Like x 1
  4. Fitzy
    Offline

    Fitzy Newly Qualified Sparky Electrician's Arms

    Location:
    Redhill
    Business Name:
    DF Electrical Services
    You could install a 3 module consumer unit fed from your 3036 board, then install an RCD and 6a mcb for the lighting circuit in this cu, which is notifiable work.

    But, by the time you’ve gone to all that effort for just 1 circuit, you’d be better off upgrading the complete board and protecting the whole house.
     
    • Like Like x 2
    • Agree Agree x 1
  5. GBDamo
    Offline

    GBDamo Regular EF Member

    Location:
    UK
    You forgot...

    ..and pray to god the existing circuit is fault free.
     
    • Agree Agree x 1
  6. GBDamo
    Offline

    GBDamo Regular EF Member

    Location:
    UK
    If done SpinLondon,s way would it still be notifiable? the OCPD at the origin of the circuit would be unchanged, only addition of additional protection.
     
    • Like Like x 1
  7. Thomas Connolly
    Offline

    Thomas Connolly Regular EF Member

    Location:
    Kent
    I figured the RCD FCU at the origin would be the simplest solution.

    As the old Wylex Fuses for lifting circuits are rated at 5a... What size fuse would I put in the RCD FCU? A 3a?

    I believe there are currently 4 pendants on the circuit.

    I don't think it would be notifiable because i would just be adding a fuse on the existing wiring, it just happens to be next to/near the fuse board?

    Correct me if I'm wrong.
     
  8. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    I would see it as an alteration to an existing circuit.
     
    • Like Like x 3
    • Agree Agree x 3
  9. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    You need to get your discrimination tables out to answer that one!
    My gut feel is that it won't discriminate.

    But, whoa fella. Why an RCD FCU?. Just install an RCD.
    You do not need any additional fusing.
     
    • Like Like x 1
    • Agree Agree x 1
    Last edited: Feb 11, 2019
  10. Welchyboy1
    Offline

    Welchyboy1 Electrician's Arms

    Location:
    Essex
    Leave it as 13a
     
    • Like Like x 1
  11. GBDamo
    Offline

    GBDamo Regular EF Member

    Location:
    UK
    I would say the fuse is largely irrelevant as it is not needed to provide protection, the fuse in the DB is doing that.

    All yo really want is an RCD.

    Slap a 13A in it.

    If such a beast existed, you could fit a non fused RCD spur.

    Tin hat on.
     
    • Like Like x 1
    • Dumb Dumb x 1
  12. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    Circuits supplying luminaires now require 30mA RCD protection.
     
    • Agree Agree x 1
  13. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    Sorry. I meant to say you just need an RCD. I’ve edited my post. :oops:
     
    • Like Like x 1
  14. Thomas Connolly
    Offline

    Thomas Connolly Regular EF Member

    Location:
    Kent
    I just thought it would be cheaper and simpler to just add an RCD FCU would it now?

    Just means I can split the existing cable, add the RCD FCU in between and be done with it?
     
  15. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    One of the problems with that idea, is the requirement is to provide RCD protection for the circuit, not just part of the circuit.
     
Loading...
Similar Threads - Advice Installation Forum Date
Domestic installation advice Electrical Forum Apr 21, 2019
Domestic New member seeking advice New Member Introductions Today at 8:35 PM

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job