Discuss ... advice on this situation please in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Evening,
Im working for a builder on a kitchen extension..

Now the usual procedure with this building contractor is do the essential checks (bonding, Ze ect) make sure its up to scratch and fit a separate board to feed my new circuits... nice and simple

However im just finishing the first fix and it turns out the client expects the house board to also be updated (rewireable fuses and no RCD protection). The builders spec doesn’t specifically ask for this so its not been included by him but hey ho its an extra for me at the end of the day.

The place is a big house and while doing a walking round it is evident that there is ongoing work by other contractors in the bedrooms and additional en suits/wetrooms. Which started last year prior to me and is still not finished.

There has been a shed load of electrical work carried out in these new suits (underfloor heating, towel rails, downlights, cabinet lighting, PIR switching/dimmers and wall lighting).

As I mentioned no RCD protection is installed so no wonder the client is fairly adamant the board change is included in my builders spec.

I asked for any certification issued to the client for works carried out but its not been done.

The work seems ok from what I can see...
Then I found metal cased double insulated wall lights in the bathrooms that have not been installed correctly with the t and e stripped and brw/blu conductors ran into the fitting (no grommet) and connected with wagos. One knock of the fittings and the case could become live with pipe work and towel rails in reaching distance.

Pulled it up as being dangerous with the client and asked why the installation was started without at the very least an RCD fitted in the first place. They said that the previous electrician who did the work was aware of the requirement for RCD protection but was told by the client that the board was being upgraded so don’t worry.

... would you put yourself in this position?
I wouldn’t

Way I see it I have a few options

1. Remove the dangerous fittings, isolate the feeds at the dimmer and risk the client reinstalling them back himself. Reinstalling them properly will be difficult as the plastic joint box and rubber cable sleave has been thrown and with the fitting being mounted on espensive tiles, hes not going to want to leave a hole where they was fitted.
Then test the lot and then do the board change.

2. Be persistent and ask for the previous electrician to rectify the lights, test the work and issue a certificate taking responsibility for the works.

3. Knock the board change on the head all together and tell the client to get the electrician back to do it and certify his work.
I have never certificated other peoples work and I really don't want to start now.

Any advice?
Cheers
 
Good advice from members, however I know how important work from builders is vital to some trade persons.

I don't understand any electrician carrying out non compliant works, on the promise it'll all be alright, don't worry.

I would suggest @youngz your works cannot proceed as is at the moment. Its a large property with various existing circuits, new works have been carried out, and some been installed non compliant, and you have been asked along with other things, to install a replacement CU.

I would also suggest, that if you wish to proceed with the work, that an EICR must be carried before any more new works are down. If you client agrees it might be useful, if this survey was done by another third party, so your not seen as making something out of this, because of the earlier issues.

If not, I would do as the others said, and decline the work.
 
Danger notice. Put something in writing to customer and builder PDQ to cover yourself and then decide how you are prepared to proceed. Sods law dictates that if anyone gets a shock you will be blamed and they will deny all knowledge of your conversations!
Good advice, if there was ever a best case of CYA this rates one of the best examples.
 
Hi - if you are unhappy with the standard of other works, then for sure don't take on the new CU. "Very happy to do the part I signed up for Gov, but ...". The fact is you've only seen what's in the open, but there could well be more to the iceberg. So I think that's a vote for option 3 :) .
 
Hi - if you are unhappy with the standard of other works, then for sure don't take on the new CU. "Very happy to do the part I signed up for Gov, but ...". The fact is you've only seen what's in the open, so there could be more to this iceberg. I think that's my vote for option 3 :) .
 
So what about you put in writing you will only certify the work you do and will not connect existing/previous wiring which is potentially dangerous. Reading between the lines I divine the previous spark has left mid job with similar misgivings. Perhaps the owner thought to finish it themselves hence the poor workmanship? Anyway in principle I go with the hive mind and would decline any work there.
 
Advise EICR and take it from there.

It's no different to changing the board any other time.

Make clear on the cert and in writing what work you carried out and what was existing at time of board change.
Along with any concerns you have.

If you cba with the hassle and have no worries about damaging your relationship with the builder and or customer just tell them you only have enough time in your schedule to carry out the previously agreed works.. then run for the hills. :)
 
I would stuck with the original plan and fit a new sub board for your circuits and leave the rest to be sorted by whoever fitted it and don't get involved with it. If client insists you change board I would walk away
 

Reply to ... advice on this situation please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
755
Hi Everyone, This is my last question/post for tonight, promise. Please can I ask for a little advice on certificates as I am now questioning...
Replies
4
Views
928
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
652
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
655

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock