Advice...Radial with boiler as a spur..what to put on test sheet

Discuss Advice...Radial with boiler as a spur..what to put on test sheet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
2
In a domestic dwelling.
I am relatively new to testing and inspection.
I came across a radial...4mm cable 16amp Type B. The washing machine is used for this radial.But somewhere in the house!!!, the boiler is connected into this circuit... The boiler has a local fused spur with 3 amp fuse.
My question is, what do i put on the sheet as the main circuit is the radial but also the boiler is another circuit joined on??
 
List it as a radial, conductor size the smallest on the circuit (likely 1.5 or 2.5 from spur?). I would also note on cert specifics. It's no different to fused spurs being present on a ring or radial socket circuit.
 
I take your point Leesparkykent thats why its confusing... My main concerns is what goes on the test sheet that i send to Napit. Kingeri The note you mention, what exactly should this say?...(my first time sending the sheets in so a bit nervous)
 
The schedule should have the csa of the cable which originates from the board, 4.0 with circuit designation noting both points.
 
I take your point Leesparkykent thats why its confusing... My main concerns is what goes on the test sheet that i send to Napit. Kingeri The note you mention, what exactly should this say?...(my first time sending the sheets in so a bit nervous)

I think the answer is sweet fa
Why would Napit want to have your test results
 
2 copies of your certificate, including schedule of test results... 1 to the person who ordered the work and 1 for your records. Napit may want to see certs. on your annual assessment, but you don't send them in. all you do is notify the job, usually on line, to Napit within 30 days of completion.
 
Nothing on the paperwork as such. Would be worth noting on the circuit schedule at the DB that the boiler is fed from this circuit for future reference.
 
I suspect the OP is using Napit's on-line certification, which when finishing the document is 'sent' to their on-line storage. Which nobody looks at, apart from you, your maker and of course your customer.
 

Reply to Advice...Radial with boiler as a spur..what to put on test sheet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock