Discuss AEG ceramic hob wiring. in the UK Electrical Forum area at ElectriciansForums.net

I assume we are talking of the final connection, between the properties fixed wiring and the appliance?

Yes you can use heat resistant flex, but not necessarily just heat resistant. Any suitable sized cable may suffice.

What does the manufacturer instructions say?
 
I assume we are talking of the final connection, between the properties fixed wiring and the appliance?

Yes you can use heat resistant flex, but not necessarily just heat resistant. Any suitable sized cable may suffice.

What does the manufacturer instructions say?
Hi it says to use H05BB-F or H03V2V2-F that withstands up to 70 degrees.
 
Standard PVC twin&earth is rated at 70degs C.
[automerge]1585496237[/automerge]
6.4KW = 27A. That is the absolute max for 2.5mm cable. I’d be looking for 4 or 6mm.
how big is the MCB for the circuit?
 
If you are talking about a short length from a cooker outlet to the hob then Toolstation sell short lengths of 6mm T&E that avoids a lot of unused wire being bought, for example 3m coil here:
Otherwise if you really want to use round cable then you can buy the HO7RNF style of cable by the meter from CEF or Superlec. I would suggest at least 4mm for a 32A circuit, for example:
 
I did have a chuckle to myself; we’ve had loads of threads on this subject.

OP’s are always told about fixed loads on radial cooker circuits, diversity etc. As been calculated, this hob would have a maximum load of 27A, less with diversity & cycling of each cooking zone.

IMO 2.5mm flexible cable will be fine, OP could probably get away with 1.5mm. He might also have difficulty terminating 6mm cable in the appliances termination box. And before anybody says anything, bootlace ferrules should be used with flexible cables in this scenario.
 
Agreed that 6mm is overkill, only suggested it as you can buy it in short coils for jobs like that. I doubt most DIY folk would find much use for the 98m or so left over from buying a reel of 4mm T&E!

In the old days you could simply but whatever type of cable you needed by the meter, even from Woolworth in the 70s and 80s! At least for some like HO7RNF that is still the case for mail order.

Also have an up-vote for suggesting bootlace ferrules, again a professional touch and a significant advantage for screw fixing fine stranded wires, but very unlikely to be seen by DIY folk.

What worries me about fitting cable that is sized for the appliance & diversity assumptions (and not for the OCPD) is what happens down the line if it simply gets reused on a new appliance. We all know it should be checked and upgraded if necessary, but how many folk outside of professional sparks or the most diligent of DIYers ever does?

Recently a mate of mine was saying his new cooker kept tripping the breaker so they had a bigger one fitted. I suspect I visibly winced when he said that as my first thought was "did anyone check what the cables were rated at?" but I know I am in a minority.
 
Last edited:
The manufacturer will always state that the appliance shall be connected by a competent person/electrician, who should know about diversity and cable sizes.

When this is not the case, the DIY’er often seeks advice, as is the case here. Don’t think you have plan ahead for the what ifs, if someone is doing something they know nothing about.
 
So loads of advice. I'm going to order 2m of 4mm2 flex from cef and some bootlace ends and fit this then I know it's right.
get the appliance first. you may need to use ring crimps.
 

Reply to AEG ceramic hob wiring. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have bought a cooker with a ceramic hob which has a warning light to show that the top is hot, the light goes out when the hob cools down. I...
Replies
2
Views
716
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
668
Have wired in a ceramic hob but find it unsuitable, now want to go back to induction hobs. Will probably buy an AEG IKE64450FB hob. As I haven't...
Replies
0
Views
835
hi looking to install a new induction hob to current wiring . the wiring i have is thick white probably about 15mm wide and is hard wired into...
Replies
0
Views
881
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock