Hi Everyone , i havnt fitted one of these before and i need to do so as a retrofit into and existing panel board. the reson for this is a down grade in their load and therefore i wish to fit a protective device to protect the current wiring against the new lower load. I also intend to fit a Voltage optimisation unit in line and by lowering their main protective device i can fit the correct size unit for their load.
1 can i simply cut a hole in a spare panel install and fix the breaker and then cut and divert the busbars via Flexis through the breaker and the unit then of to their load ?
2 is their a good place to go and get some training ( is it needed or as they as simple as they look )

Thanks for taking the time to answer
kev
 
Why are you installing an Air Ciruit Breaker?
Why not use an MCB?
If you do install it, just use an enclosure to house the ACB, break into the tails between the meter and the CU, connect the ACB, then from the ACB to the optimisation unit, then to the CU.
To be honest, it would probably be simpler to det the DNO in to down rate their fuse.
 
Hi Spin , like the bike !
They are currently pulling 625 amps peak per phase , i wasn't aware they made MCB's that large. I have contacted the DNO however their is no fuse between the sub and the incoming supply , they are an integral part of a loop main ( i think ) their is 8 large tails feeding into the bottom of their switch gear going directly to the customers main switch and then Bars. So thought the best way would be to install an ACB.
However im open to suggestions
thanks again
 
What current are we looking at? I don’t like the idea of flexibles in switchgear due to very high possible fault currents. I’ve seen bus bars bent due to fault currents, flexibles will jump about like zebedee.
Some ACB’s can be down rated without the need to change the unit.
Can you give more details?
Make, model, current, etc.
 
Hi Spin , like the bike !
They are currently pulling 625 amps peak per phase , i wasn't aware they made MCB's that large. I have contacted the DNO however their is no fuse between the sub and the incoming supply , they are an integral part of a loop main ( i think ) their is 8 large tails feeding into the bottom of their switch gear going directly to the customers main switch and then Bars. So thought the best way would be to install an ACB.
However im open to suggestions
thanks again
Sorry, thought you were doing domestic and instaling one of those Vphase optimisation units.
No ACBs are more appropriate.
As Tony says, we would need a lot more information, probablly some photos of the existing switch gear and panels.
 
Last edited by a moderator:
Hi We are looking at a maximum current drawn of 625 amps per phase , so I need to allow for approximately 750 amps per phase. I would be retrofitting the ACB into the existing panel board. At the moment all they have is a main switch which is rated at 1200 amps fed direct from the sub station next door this goes direct on the bus bars and these feed directly of to switch fuses and then on to sub mains to different parts of the factory.
The existing panel board is approximately 20 - 30 years old
thanks
 
thanks very much , however the existing gear is simply a large main switch with vertical bus bars at the rear of the chamber . above the main switch their is a spare panel with a spare void behind where i could mount an ACB within ( there is loads of room). behind this is the bus bars ( their must be at least 3 feet behind the cover plate to the bus bars ).
I dont have any photos unfortunately.
May i ask are you suggesting using copper bar to bolt on to rear of the ACB from the existing bars and then diverting back to the bars in bar again? Or do you have a better suggestion of cable to use ? or even indeed a recomended manufacterer i could contact for help on this point
thanks again for your help
 
Most ACB’s will be adjustable down to 75% FLC (some even lower) which would give 900A
I really can’t understand the need to down rate the protection to the board. It won’t affect the loading on it so billing won’t be affected. The ACB is there just to protect the boards bus bars.
 
hi guys
At the moment their is no overcurrent protection between the bus bars and the sub station.
I am looking to fit a voltage optimisation unit in between the sub station ( via the main switch) and the bus bars . therefore in order to protect this unit and the wiring to and from it i will need to install some sort of overcurrent protection device. This is why i was thinking of retrofitting and ACB into the existing panel board system. Obviously i dont want to fit a unit that is to large as they are very costly so if i can down grade the wiring with an ACB to suit their current load plus 20% for expansion the whole thing works.
hope fully this explains it a little clearer
thanks again
 
No disrespect, but i don't think your competent to be mucking around with a switchboard of this size going by your above proposals!! You need to maintain the switchboards fault current ratings bracing, so you would know flexible and bracing is a contradiction. You also don't cut into a switchboard and start altering or cutting into bus bars unless you know exactly what your doing of..

The 1200A ACB may also have connections to protective relays, have you checked?? That ACB IS the over current protection between the transformer and the bus bars !! As Tony has already told you ACBs of this size have a wide setting arrangement in many cases down to 60% or less. I'm also guessing that you also have little idea how to set or reset the parameters of the protection curves on an ACB

There is no need to replace this breaker anyway, as it's there to protect the bus bars and possibly the transformer, not the outgoing cable/loads, they will be protected by the distribution MCCBs or switch fuses...

Let me put it another way, an electrician shouldn't be making these sorts of dicissions on a sub-station supplied main switchboard, that is the work of a qualified Engineer...

Mark my words here, get something like this wrong, and you'll know all about it, ...but fast!!
 
i have to agree witbh the others. Setting an ACB to cascade with the DNO's gear will require extesnive knowledge and experienceof protection devices. Also, as theyve mentioned, you have overcurrent protection to your Busbars in the panel, and so you can then feed final circuits or submains from other protective devices that are tapped from the busbar.
 
I’ve seen the aftermath of over stressed bus bars. Lumps bitten out of 8” X 3/8” copper isn’t a pretty site. The bars have to be supported and braced to withstand the tremendous magnetic forces between them under fault conditions.

You still haven’t said what make the ACB is or the switchboard.
 
Apart from anything else Tony, when people don't understand the ''From build'' of a switchboard, that Form build level can be destroyed when you start mucking about with internal dividing sections etc within the panels. A high Form 4 panel can easily be reduced to a Form 1 around that ACB.

It's also not just a question of fabricating a Bus Bar arrangement, that's the easy part, the bracing of those bus bars to the switchboards KA fault level, can be neigh on impossible. You can't just bolt them to the dividing panels, they have to be bolted to the main panel structures. Or as you say, in a fault the snaking bars will take those thin panels with them ...lol!! Switchboards are designed AROUND the required KA fault level, to which it can be potentially subjected...

We don't know what size the supplying transformer is, but a 1MVA TX can quite easily supply 20+ KA into a fault, and for a considerable time too, if the protection hasn't been set correctly!! This is Not something an electrician should be contemplating off his own back, this needs an Engineers involvement, as well as the manufacturers of this Switchboard.
 
Last edited by a moderator:
No disrespect, but i don't think your competent to be mucking around with a switchboard of this size going by your above proposals!! You need to maintain the switchboards fault current ratings bracing, so you would know flexible and bracing is a contradiction. You also don't cut into a switchboard and start altering or cutting into bus bars unless you know exactly what your doing of..

The 1200A ACB may also have connections to protective relays, have you checked?? That ACB IS the over current protection between the transformer and the bus bars !! As Tony has already told you ACBs of this size have a wide setting arrangement in many cases down to 60% or less. I'm also guessing that you also have little idea how to set or reset the parameters of the protection curves on an ACB

There is no need to replace this breaker anyway, as it's there to protect the bus bars and possibly the transformer, not the outgoing cable/loads, they will be protected by the distribution MCCBs or switch fuses...

Let me put it another way, an electrician shouldn't be making these sorts of dicissions on a sub-station supplied main switchboard, that is the work of a qualified Engineer...

Mark my words here, get something like this wrong, and you'll know all about it, ...but fast!!

Thanks very much Engineer 54 , i appreciate your comments and take your advice on board. However their is one point you are missing . their currently is no ACB or any protective device installed between the bus bars and the sub station only a 2000 amp main switch. other than the switch it is a direct connection between the bars and and the loop main from the substation.

With regards to the final design im happy to hand this over to an engineer to specify it correctly , but I wanted to give him or her some idea of my proposals before I did this by gauging peoples opinion on here.
but thanks again
 
Where do these 3m of tails connect to in the substation, directly to the Transformer or to a LV DNO Switchboard??
I can't believe there is absolutly no protection provided between the TX LV terminals and your unprotected main switch!!! Loops as you call it, are normally only seen at the MV/HV side of transformers, by means of RMU's (Ring Main Units)....

My advice, is to get a Qualified Electrical Engineer involved in your planned project now, tell him your requirements, and let him make the dicissions on how to go about achieving them in a cost effective way... Or, Panel manufacturers can also be given the task of providing your needs. Who will send an Electrical Engineer to assess what you have, and what you need and propose a design to meet them, based on/around their panel systems... You could ask 2 or three such manufacturers to quote on your project.
 

Reply to Air Circuit breakers in the Electricians' Talk | All Countries area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock