Hi.

Been reading the but around 427.1.7.

Does anyone have any idea on retrospective application?

Is this going to apply to every board change or just adapted to new builds and then as a C3 recommendation for everything else?

Given prices it's going to be a massive cost change on a board swop. Plus, I know for certain I'm going to have space issues with anything over 30 years old here in Fife.

Thoughts?
 
isn't that the sdame for an afci?
Not quite.

An RCD will detect a "parallel arc" between L & E, as well as simple leakage due to non-arcing conduction. But it won't detect a fault between L & N (that is below the OCPD) nor a series arc where a small break in L or N has happened.

An AFDD should pick up the high frequency content of the arc and so trip on L-N faults and series arc faults. But other things also produce arc noise.
 
Not quite.

An RCD will detect a "parallel arc" between L & E, as well as simple leakage due to non-arcing conduction. But it won't detect a fault between L & N (that is below the OCPD) nor a series arc where a small break in L or N has happened.

An AFDD should pick up the high frequency content of the arc and so trip on L-N faults and series arc faults. But other things also produce arc noise.
thx PC
i had thought the main component was the same, a toroid .......at least to the extent of my reading......

as ro the 'frequency' and/or arc waveform, we're told our AFCI incorporates a microprocessor with special algorithm software

the details of which, we're not privy to, but the testing lab methods we are>>>

This is what they used....a 'simulator;'.....

https://i.Upload the image directly to the thread.com/eOF06wB.jpg
Do RCD's have this manner of testing?

~S~
 
The AFDD probably have a toroid as well, but it would need to be another in (probably) the L so it can detect the faults that a RCD is designed not to (L-N flow). By frequency I mean a typical earth faults sees a lot of 50Hz flow, but an arc typically has components to over 10kHz.

As far testing - that is a sore point. In the UK electricians typically have a Multi Function Tester (so high voltage IR, few 100mA bond resistance, supply Zs, RCD trip, voltage, and probably phase rotation, maybe earth rod impedance via two spikes, etc) but I have not seen much sign of them being available to test AFDD. We are being told to trust the self-test button, etc. Yes, what a good idea...
 
If they don't work on ring circuits and not required over 32amp and ineffective on lighting circuits afdds seem pointless.
I can see some cases for them, but the cost/benefit looks very poor to me.

They do work on RFC but don't detect an open ring as practically no arcing takes place there as voltage difference is very small, however, they should detect arc faults on appliance cables that are attached that are above the few amps threshold.

But again, where is the evidence for their use? That is a proper analysis of fire (or near fire fault) cases that clearly would have been stopped by an AFDD and not things like lint fires in tumble dryers, etc.
 
I can see some cases for them, but the cost/benefit looks very poor to me.

They do work on RFC but don't detect an open ring as practically no arcing takes place there as voltage difference is very small, however, they should detect arc faults on appliance cables that are attached that are above the few amps threshold.

But again, where is the evidence for their use? That is a proper analysis of fire (or near fire fault) cases that clearly would have been stopped by an AFDD and not things like lint fires in tumble dryers, etc.
I agree, I know alot of electrical fires are due to faulty white goods, there has been talk that it is in fact the white goods industry are pushing for us to incorporate AFDD to protect plugged in equipment.
It all seems like a box ticking exercise to me, there's no data I'm aware of.
 
I agree, I know alot of electrical fires are due to faulty white goods, there has been talk that it is in fact the white goods industry are pushing for us to incorporate AFDD to protect plugged in equipment.
It all seems like a box ticking exercise to me, there's no data I'm aware of.
Maybe we should be pushing for the white goods industry to stop throwing cheaper & cheaper components into their appliances then we wouldn't have this problem!
 
I can see some cases for them, but the cost/benefit looks very poor to me.

They do work on RFC but don't detect an open ring as practically no arcing takes place there as voltage difference is very small, however, they should detect arc faults on appliance cables that are attached that are above the few amps threshold.

But again, where is the evidence for their use? That is a proper analysis of fire (or near fire fault) cases that clearly would have been stopped by an AFDD and not things like lint fires in tumble dryers, etc.


Funny you mention evidence. In the US, other than cut wire wrapped in glass tape and hooked up to a neon gas transformer in a laboratory there is zero evidence that arcing is behind any residential fires to begin with.

There is the case of firefighters opening walls to find smoldering studs with romex stapled across them. However, pyrophoric carbonization from an energized staple likely to be the real cause behind these events was and is miss-theorized into arcing. Ignoring the evidence of dried wood around nails and the foundation some distance from the smoldering area indicative of low level current leakage over the years and not arcing.
 
Thats what the plug top fuse is for, literally. A short in the flex will open the fuse within 3 cycles. Though anyone here can correct me on that if not so in practice.

A 13A fuse won't blow on an arc fault though. A fuse takes a relatively long time to open.
 
Maybe we should be pushing for the white goods industry to stop throwing cheaper & cheaper components into their appliances then we wouldn't have this problem!
And that is the problem, accordingly to what I've heard, committee that wrote the standards are made up manufacturers, in white goods industry.
 
Last edited:
Thats what the plug top fuse is for, literally. A short in the flex will open the fuse within 3 cycles. Though anyone here can correct me on that if not so in practice.
I understood that an AFDD should be detecting an intermittent rapid change in current e.g. a loose connection in L or in N that is arcing (and which would likely not blow any fuse).
 
Do have a time current curve to common BS1363 fuses?
Here is the typical plot, not as well defined as BS88 fuses:
BS1362FusingTime.png
 
I understood that an AFDD should be detecting an intermittent rapid change in current e.g. a loose connection in L or in N that is arcing (and which would likely not blow any fuse).


A parallel L-N or L-E event will blow the fuse.

A series event without an outer screen to earth itself out to would technically require an AFDD, however, I do not believe partially severed cords are behind any number of fires. I aslo do not believe that AFDDs accurately detect dangerous arcing. Cost effective AFDDs will always be a compromise between tripping on dangerous arcing and not tripping on electronics, vacuums, drills and the like. All to often one is indistinguishable from the other and the 1.5-5 amp series current pickup is part of that compromise.
 
A parallel L-N or L-E event will blow the fuse.

A series event without an outer screen to earth itself out to would technically require an AFDD, however, I do not believe partially severed cords are behind any number of fires. I aslo do not believe that AFDDs accurately detect dangerous arcing. Cost effective AFDDs will always be a compromise between tripping on dangerous arcing and not tripping on electronics, vacuums, drills and the like. All to often one is indistinguishable from the other and the 1.5-5 amp series current pickup is part of that compromise.

A brief L-N arc event will not rupture a 13A fuse.
 
A brief L-N arc event will not rupture a 13A fuse.


From what I understand (and could be wrong) a 32 amp MCB has a max Ze of 1.15 ohms or 200 amps of perspective fault current at the furthest point of the socket. 200/13 would be 15 times the rating. Thus 200 amps trips a TDC180 British plug to fuse in under 0.01 seconds.

https://www.eaton.com/content/dam/e...s/data-sheet/eaton-tdc180-fuse-data-sheet.pdf

This is assuming TDC180 fuses are of the same kind used in the UK.
 
This is assuming TDC180 fuses are of the same kind used in the UK.
From above curve, worst-case it is 0.03s at 200A PFC.

I guess the real question is what sort of fault will start a fire but only an AFDD will trip, and how common/likely are they?

In my limited experience of sorting out fixed wiring, the only two cases of a long-term serial arc were light bulb holders in the days of 60W/100W lights and you could sometimes here the buzzing and see the light dim slightly. Yes, those are circuits for which AFDD are not recommended...
 
Does anyone know the figures for the improvement from fitting these devices in Germany? I can't see how any figures could be of value as if a competent person installs an AFDD board they are also going to check the condition of the installation and could remove fire hazards skewing the results.
 

Reply to Amendment 2 and AFDD's in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock