A 13A fuse won't blow on an arc fault though. A fuse takes a relatively long time to open.
Do have a time current curve to common BS1363 fuses?
The flex itself typically adds only a small amount if impedance to the fault loop.
Discuss Amendment 2 and AFDD's in the UK Electrical Forum area at ElectriciansForums.net
A 13A fuse won't blow on an arc fault though. A fuse takes a relatively long time to open.
Installing the AFDD at the socket outlet is surely an acknowledgement that white goods are the main issueAnother difference between the UK and the USA.. UK installs AFDD in the distribution board, where as the USA favours them at outlet sockets.
I understood that an AFDD should be detecting an intermittent rapid change in current e.g. a loose connection in L or in N that is arcing (and which would likely not blow any fuse).Thats what the plug top fuse is for, literally. A short in the flex will open the fuse within 3 cycles. Though anyone here can correct me on that if not so in practice.
Then why not have them fitted to the appliance plug? They can bear the cost if they think it is important...And that is the problem, accordingly to what I've heard, committee that wrote the standards are made up manufacturers, in white goods industry.
Here is the typical plot, not as well defined as BS88 fuses:Do have a time current curve to common BS1363 fuses?
I understood that an AFDD should be detecting an intermittent rapid change in current e.g. a loose connection in L or in N that is arcing (and which would likely not blow any fuse).
A parallel L-N or L-E event will blow the fuse.
A series event without an outer screen to earth itself out to would technically require an AFDD, however, I do not believe partially severed cords are behind any number of fires. I aslo do not believe that AFDDs accurately detect dangerous arcing. Cost effective AFDDs will always be a compromise between tripping on dangerous arcing and not tripping on electronics, vacuums, drills and the like. All to often one is indistinguishable from the other and the 1.5-5 amp series current pickup is part of that compromise.
A brief L-N arc event will not rupture a 13A fuse.
From above curve, worst-case it is 0.03s at 200A PFC.This is assuming TDC180 fuses are of the same kind used in the UK.
From above curve, worst-case it is 0.03s at 200A PFC.
I guess the real question is what sort of fault will start a fire but only an AFDD will trip, and how common/likely are they?
In my limited experience of sorting out fixed wiring, the only two cases of a long-term serial arc were light bulb holders in the days of 60W/100W lights and you could sometimes here the buzzing and see the light dim slightly. Yes, those are circuits for which AFDD are not recommended...
It's an interesting point this.Considering an RFC is 2 conductors in parallel, an arc in one leg is strictly speaking bridged out by the other leg. So theoretically there should be no arc on the damaged leg? Am I missing something here?They do work on RFC
It wont work on a RFC if there is just a loose connection on the RFC. But will/should work on a series arc from socket to appliance. Providing the load after the arc is 2.5amps (1.5amps For Electrium devices).It's an interesting point this.Considering an RFC is 2 conductors in parallel, an arc in one leg is strictly speaking bridged out by the other leg. So theoretically there should be no arc on the damaged leg? Am I missing something here?
OK. This is the part I want to get straight in my head. Is it more correct to say then that arcing in the fixed wiring of an RFC won't be detected while arcing in appliances connected to an RFC will likely be detected?It wont work on a RFC if there is just a loose connection on the RFC. But will/should work on a series arc from socket to appliance.
My local wholesaler is £165 + vat for a wylex afdd rcbo , and they are special order not a stock item at the momentNice units by Wylex, but still £150 a pop at the moment.
Screwfix £150 in stock.My local wholesaler is £165 + vat for a wylex afdd rcbo , and they are special order not a stock item at the moment
Only availble for next day collection at the branches near meScrewfix £150 in stock.
Not yet,most of them are for individual circuitsSo is there no AFDD which can be installed and protect multiple circuits (like an RCD on a dual split board for instance)?
Helpful link. Confirming then what we suspected, that RFC fixed wiring is not protected against a series arc, except in the extremely unlikely scenario of 2 arcs taking place simultaneousely.Hager has a document claiming that they work on RFC's but acknowledge that only if the fault is on a spur or appliance connection
You may well be right. But it could just as easily happen that the introduction of the AFDD ends up heaping more negative press on the RFC due to its inherant unsuitability for an AFDD protected circuit compared to the radial, which does not share these limitationsSo it might be a case that really they only get used for sockets, in which case I foresee the return of a single/dual RFC per property!
No, you are not understanding the RFC limitation on AFDD.You may well be right. But it could just as easily happen that the introduction of the AFDD ends up heaping more negative press on the RFC due to its inherant unsuitability for an AFDD protected circuit compared to the radial, which does not share these limitations
I don't think I, m misunderstanding it. The "open ring" won't detect an arc. The "open radial" will detect an arc.No, you are not understanding the RFC limitation on AFDD.
It depends on how the "powers that be" promote the AFDD. Over here the the protection afforded to the fixed wiring is emphasised as heavily as the protection afforded to the appliances connected to the fixed wiring. Like you I don't have any major concerns about arcing in a ring circuit as I have not experrienced(nor yet been presented with) credible evidence for series arcs in fixed wiring causing fires. But I, m simply making the point that the introduction Aof the AFDD is unlikely to enhance the ring circuits appeal (with exception of UK)So you might see that as a limitation on detecting faults,
Yes...but due to the open ring having practically no arcing.I don't think I, m misunderstanding it. The "open ring" won't detect an arc. The "open radial" will detect an arc.
Agreed, if it is for appliances then RFC or radial makes no difference.It depends on how the "powers that be" promote the AFDD. Over here the the protection afforded to the fixed wiring is emphasised as heavily as the protection afforded to the appliances connected to the fixed wiring.
The RFC (in this context) only makes sense with fused plugs, and really only the UK and countries with a shared electrical history use the BS1363 plugs so the discussion is limited to them anyway.Like you I don't have any major concerns about arcing in a ring circuit as I have not experienced (nor yet been presented with) credible evidence for series arcs in fixed wiring causing fires. But I, m simply making the point that the introduction of the AFDD is unlikely to enhance the ring circuits appeal (with exception of UK)
Those that I've seen (Crabtree & Wylex) are single module RCBOs, with AFDD incorporated.
Where is it stated they should not be used on shower cats?I did read over the proposed amendment and AFDD are not being pushed for lights or high current loads like showers. Odd really, as most seriously burned out examples I have seen have been shower circuits, but maybe good old fashioned resistance and so no arcing to make one trip?
So it might be a case that really they only get used for sockets, in which case I foresee the return of a single/dual RFC per property!
I did read over the proposed amendment and AFDD are not being pushed for lights or high current loads like showers. Odd really, as most seriously burned out examples I have seen have been shower circuits, but maybe good old fashioned resistance and so no arcing to make one trip?
So it might be a case that really they only get used for sockets, in which case I foresee the return of a single/dual RFC per property!
Fair point. You have legitimately turned that around into an arguement that the RFC is safer than a, radial from an arcing point of view?Yes...but due to the open ring having practically no arcing.
It sounds very much like the arcing is a good thing here!!!
It does not, but it said something like "circuits not exceeding 32A" which rules out many modern electric showers over 7kW or so.Where is it stated they should not be used on shower cats?
Or return to the old Wylex board style of double screw terminals?Perhaps we should install all power circuits with parallel conductors. For another amendment/edition, all accessories could include another live terminal for high integrity supplies.
I'm a big supporter of that, particularly on the main switch terminals.Or return to the old Wylex board style of double screw terminals?
Wouldn't any downstream AFDD that was loaded detect this and switch off. The current passing through the AFDD will be varying with an arc's signature whether the arc is before or after it.And nothing protects against THIS!
Big shout out to SPN who were brilliant yesterday. Onsite in under 90 minutes. Fixed in 30 more.
That assumes it was arcing, and not just a few tens of mOhm resistance heating.Wouldn't any downstream AFDD that was loaded detect this and switch off. The current passing through the AFDD will be varying with an arc's signature whether the arc is before or after it.
Yes. And not even a few tens of ohms is required. A half ohm (poorly tightened main fuse) will produce 30 Watts of heat in a fuse enclosure under full load. . Added to the heat produced by the fuse under normal working circumstances.That assumes it was arcing, and not just a few tens of mOhm resistance heating.
I was talking of milli-ohms.Yes. And not even a few tens of ohms is required. A half ohm (poorly tightened main fuse) will produce 30 Watts of heat in a fuse enclosure under full load. . Added to the heat produced by the fuse under normal working circumstances.
My error. Never saw the little "m". Next stop.. specsaversI was talking of milli-ohms.
Say 50A (shower and/or cooker) & 0.05 ohm = 125W