Hi.

Been reading the but around 427.1.7.

Does anyone have any idea on retrospective application?

Is this going to apply to every board change or just adapted to new builds and then as a C3 recommendation for everything else?

Given prices it's going to be a massive cost change on a board swop. Plus, I know for certain I'm going to have space issues with anything over 30 years old here in Fife.

Thoughts?
 
Perhaps we should install all power circuits with parallel conductors. For another amendment/edition, all accessories could include another live terminal for high integrity supplies.
Or return to the old Wylex board style of double screw terminals?

The Wago style of spring loaded ones were something I looked at with deep suspicion when they first came out, but it turns out they (with clean cable, etc) give a good reliable connection and no need for someone to have either proper experience and training, or to have and use a torque screwdriver to get reliable connections.
 
And nothing protects against THIS!

Big shout out to SPN who were brilliant yesterday. Onsite in under 90 minutes. Fixed in 30 more.
 

Attachments

  • IMG_20211110_140635868.jpg
    386.4 KB · Views: 35
  • IMG_20211109_114744656.jpg
    596.9 KB · Views: 34
  • IMG_20211110_151351983.jpg
    330.9 KB · Views: 34
And nothing protects against THIS!

Big shout out to SPN who were brilliant yesterday. Onsite in under 90 minutes. Fixed in 30 more.
Wouldn't any downstream AFDD that was loaded detect this and switch off. The current passing through the AFDD will be varying with an arc's signature whether the arc is before or after it.
If all loads were AFDD protected, the current through the cut out would fall to zero and the resistive heating would stop.
 

Reply to Amendment 2 and AFDD's in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top