Hello,

I was thinking of getting this consumer unit replaced as it is made of plastic, the lid doesn't really close properly, it hasn't been tested in awhile and I had to have my ringdoor bell supply put into another box as there was no space.

Do you think it is worth it to get a new one?
 
View attachment 58666

Hello,

I was thinking of getting this consumer unit replaced as it is made of plastic, the lid doesn't really close properly, it hasn't been tested in awhile and I had to have my ringdoor bell supply put into another box as there was no space.

Do you think it is worth it to get a new one?

My personal opinion would be to get a EICR done, which will tell you if the whole installation is safe or not. The fact that is is plastic doesn't mean it needs to be replaced with a metal one provided it meet the regulations at the time it was installed.

It seems strange to me that a ring door bell had to be put on its own circuit, and could not be taken from a F.C.U from the socket circuit, although I am not an expert

I would also consider swapping the lighting MCBs for RCBOs to provide a bit of extra protection.
 
View attachment 58666

Hello,

I was thinking of getting this consumer unit replaced as it is made of plastic, the lid doesn't really close properly, it hasn't been tested in awhile and I had to have my ringdoor bell supply put into another box as there was no space.

Do you think it is worth it to get a new one?
Your CU complied at the time that your dwelling was wired, as you wish to add a new circuit and there isn't any space for a new cir, may be now is a good time to change it.

It looks like a recessed unit, which will not be a straightforward installation, in my opinion, your best option will be to employ an Electrician, don't buy stuff Willy Nilly, as an Electrician will know what is required, and you could waste money on something that is inappropriate for the job, get several quotes, and don't opt for the cheapest one just yet, get the quotes and post them on here, erasing the persons details , where there will be lots of people who can judge the best option , good luck please let the forum know how you get on. One more thing Make sure the quotation includes "Notification if required and an EIC "Electrical Installation Certificate" don't shell out any money until the job is complete and the cert EIC has been received. Again good luck
 
Last edited:
View attachment 58666

Hello,

I was thinking of getting this consumer unit replaced as it is made of plastic, the lid doesn't really close properly, it hasn't been tested in awhile and I had to have my ringdoor bell supply put into another box as there was no space.

Do you think it is worth it to get a new one?

If this was my own property I would replace the MCB's which aren't protected by RCD with RCBOs and check all terminations for being correctly made, I would leave the plastic box as it is.

I would advise a customer to do the same and have an EICR carried.
 
Obviously you have various reasons to think about replacing it and generally that is a good idea as you can end up with a better overall installation in terms of reliability & safety.

#1 consideration has to be getting any work done in a safe and professional manner, and you might find folk on here that you can get help from if they are local.

As already said, it is worth looking at an EICR first to identify anything that is worth considering as part of the changes. But the aspects that are most beneficial (at least in my opinion) are:
  • Having an all RCBO setup so faults on any circuits are clearly identifiable and only impact on that circuit.
  • The new CU has sufficient space for a couple of extra circuits should you need them in the future.
  • These days it is common to have a surge protection device (SPD) in the CU to reduce the risk of damage to electronics from lightning or other surges.
  • A metal enclosure with the appropriate glands is far better in terms of fire safety.
So when thinking about such work, try to think of anything you would want in the future, or anything that might be practical to do (e.g. if the CU is currently inaccessible or in a place you would like to use for something else). If you are interested there are some guidelines here:

Number 1 and 4 are relevant here. As already said, this is not a trivial bit of work so do your research on finding someone who does a good job first.
 
Good Man nice to see someone that listens to advice.

I have no clue about electrical stuff so want to do it as safely as possible! I'd never attempt to do it myself.

I only noticed it hadn't been inspected for a long time the other day, as I was trying to figure out why the lights weren't working in one room, but turned out it was just the old bulbs had failed (honestly not sure if it was one at a time or if they all blew together) which I have replaced with some LED ones now
 
I have no clue about electrical stuff so want to do it as safely as possible! I'd never attempt to do it myself.

I only noticed it hadn't been inspected for a long time the other day, as I was trying to figure out why the lights weren't working in one room, but turned out it was just the old bulbs had failed (honestly not sure if it was one at a time or if they all blew together) which I have replaced with some LED ones now
In my opinion, Whilst an EICR is a good idea, part of the rules regarding a CU change advises that an EICR part of the Process of a CU SWAP " see the best practice guide published by the ECS Electrical Safety Council" says, or advises that an EICR, is carried out PRIOR to the swap to ensure your installation is safe.

So it my be prudent to insist on this test, in any case. it may cost you more but better be safe than sorry.

Plenty of Cowboys out there that will just do the minimum.

The EIC on completion of the CU Swap should prove your installation is safe and sound, and fit for purpose.

Let the Forum know how you get on, lots of interested parties I'm sure.
 

Reply to Any point getting this consumer unit replaced? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
I have a fairly recently installed consumer unit with an RCD, between it and the garden there is another, much older (25yrs?) RCB (big Wylex...
Replies
11
Views
2K
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K
I had a consumer unit replacement today. It was a bit of a nightmare as most of the cables were too short for the new unit. I extended the ones...
Replies
24
Views
6K
Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock