Hi chaps,

Could any of you help me out with this one please as I don't usually do apartment blocks and haven't come across this scenario before.

Large apartment block built 2004. Looks like the tails enter the consumer unit via Armoured cabling with the armour being used as the main earth & bolted to the top of the metallic CCU (can't confirm as the CCU is up to the ceiling). PSCC = 0.56ka. The linking cable from the SWA bolt to the earthing bar is 4mm2. Now (not taking the earth bar securing/earthing screw to CCU into account) my calculations suggest the size is adequate. But with the tails looking like 10mm (hard to tell as they are is soft flimsy sheaving) my understanding is that 4mm linking cable should be at least 10mm2 to meet the regs.

Anyone tell me if I'm wrong or, as I'm never wrong! ;-) what code it would be. I'm thinking C2?

Cheers,

IMG_20180613_122505 b.jpg
 
Presumably they have thought that glanding the cable to the board is providing the earth, but is that connection secure?
Therefore you now have a (section of) the earthing conductor at 4mm², adiabatically this is OK for a TNS system and a 60A main fuse, if this is what you have. If it is a bonding conductor as well then you are out of luck even with the SWA armour.
If you are selecting the size from the table then it would need to be 10mm². No code I think so long as the connection is secure and "mechanically and electrically sound"
 
Are you doing an EICR? I assume that the SWA is original being from the time of cable colour harmonization. What is the Zs at the switch-fuse? it could be a high resistance due to poor metal to metal contact with the glands. Did you do a test on the gland thread coming into the consumer unit?
 
Are you doing an EICR? I assume that the SWA is original being from the time of cable colour harmonization. What is the Zs at the switch-fuse? it could be a high resistance due to poor metal to metal contact with the glands. Did you do a test on the gland thread coming into the consumer unit?

Hi Anthonybragg,
Yeh an EICR (ergo why posted in the eicr forum :p ).
My assumption is everything is original with no signs of modifications. Building is only 14yrs old.
By the switch-fuse I assume CCU main linked switch? in which case it was ok (0.34 off the top of my head).
I couldn't inspect the gland thread as it was above the ceiling (which i guess is a fault in itself) but the nut was tight.
 

Reply to Apartment block main earth size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827
I have just carried out an EICR at an old property and found this issue with the main earthing conductor. It has a TN-S system but the earthing...
Replies
32
Views
5K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hello Experts Need some advise please, due to getting conflicting information from electricians. Background info: 4 years ago done the whole...
Replies
3
Views
3K
Another question! I'm designing for a TT system, there's going to be one 10 way Rcbo consumer unit for the house, less than 3 metres away from...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock