Discuss Apollo Gem my experience! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

F

FrederickW

With 8.5 KW of PV, two hot water cylinders and a meter spinning faster in reverse than it ever does forward it was obvious that something had to be done and I am not referring to the meter. lol (backstop fitted unfortunately)
There now seems to be a dozen or so excess power diverters of one kind or another on the market. Which one to choose? For me that was not too difficult as there was only the Gem that ticked all the boxes.
My single phase supply cabinet is fitted to an external garage, 20 metres from the house from where sub mains distribute power to house, workshop and barn. With no way to run a cable for the CT other than cutting through concrete it had to be wireless.
I looked at the iBoost which I came across on here, but it only has one proportional output, which would not have best suited the power and load I have available. I had pretty much resigned myself to the iBoost when after several google searches for immersion controllers I came across the Apollo Gem. It’s always a concern when finding a product like this which has no customer web comment one way or the other. After reading the bad customer service comments relating to the solar immersion it did make me think twice. I read the product and tech info on their web site and was quite impressed with the install manual, it would do (on paper at least) what I require.
I listed a few questions to which I couldn’t find answers to and gave them a call. I wasn’t parting with any of my hard earned without speaking to someone first! The phone was answered promptly and I stated that I have some technical questions; fortunately someone was available so I did not have to wait for a call back. I asked about transmitter range explaining the site conditions (I have wireless security that won’t do the distance without a repeater), OK difficult question for a definite answer. Long and short is I can extend the CT wire six meters and mount the transmitter externally if necessary. The chap was very helpful and assured me that I would not be disappointed with the product. OK then, sold!
Delivered day after payment, before I had the chance to get the other installation bits. Kid with a new toy can’t wait to take it apart. All in all it’s OK, professionally made mostly surface mount. Good build quality, switching devices rated at 16 amp each and two paired per channel.
Installation was easy enough, fixings supplied, rear or bottom knockouts easy to remove. Would have liked more cable room to accommodate my gorilla mits!
Now to range, it would not work from inside the garage, that was asking too much so I had to mount the transmitter on the outside wall in an IP65 enclosure (Gewiss GW40101). Even so its range is quite staggering. 32metres, 1 window and 3 internal block walls to the receiver, showing full signal strength!
Set up was easy to do, it worked out of the box, just had to enable channel 2 and input load values.
So far the system has been operational for two weeks, in which time 225 KWhr have been diverted between one immersion and a 2.55 KW storage heater. My other DHW tank is on a timer set between 12.00 and 14.00. There is currently hot water available in the morning and at times we have had to have the door and window open because of the dammed storage heater! I know/hope that will soon change. All it has to do now is prove to be reliable. There is a five year guarantee although I am always sceptical with such offers, guess I am one of the guinea pigs. So far on the basis of my experience with the company and the product I am very pleased.
 
Last edited by a moderator:
...its range is quite staggering. 32metres, 1 window and 3 internal block walls to the receiver, showing full signal strength!

I've just fitted an Apollo GEM (aka GEM-D) in a similar situation where the supply arrives in a farm shed and I've got full 9/9 signal over 45m to my house. I was careful to fit the transmitter behind a lath & plaster wall in the shed and the other end on a wall opposite a window (in a wooden cupboard), but it's still impressive. Before I fitted it, I walked the controller around my farm-yard on an extension lead, and I could only degrade the signal to 8/9 when I took it into a a block-built garage 40m from the transmitter.

I also got this helpful info about range from Apollo, in reply to a query: Without obstacles, range could be 500m. If you have a weaker signal, there's an undocumented check for packet loss to determine whether it's still workable. Press up or down from the home display, and the 4th (last) line of the 2nd main display looks like this:
Signal: 9 000 HHHH hh
where HHHH is the channel ID (in HEX) and hh is the packet sequence number. hh should increment regularly (about once per sec), but a pause then a double increment implies a loss. Too much loss and the link becomes unusable.

I can confirm everything else Fred said about the product, which I'm using in a very similar scenario. I also chose it over the iBoost 'cos I wanted two outputs. I'm powering top then bottom coils in one large tank, which works really well so far - quickly up to temperature in an hour or so then more volume throughout the day if poss. I also chose the Apollo GEM 'cos it has two outputs. The Immersun also has two outputs, but the Apollo GEM cuts in at a lower export power (it says 70W in the specs, whereas the Immersun claims 100W. My intuition says this small amount should make a significant difference with variable sunlight on cloudy days.
 
Boris for PM( after we get out ot the eu).
 

Reply to Apollo Gem my experience! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello fellow sparks, I’m looking to do my testing and inspection course which starts on the 30th of April, but I have not got much testing...
Replies
0
Views
242
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
780
Advice if you please - We have 8kw of solar feeding into a Powerwall 2/Gateway with a 3 phase system. I wish to divert some of the surplus power...
Replies
0
Views
825
Hello, I need to conduct interviews with experts in the relevant field for my university project. The topic and product that I’m developing a...
Replies
24
Views
2K
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
292

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock