I'm trying to determine the appropiate load to install a separate oven and ceramic hob (in a domestic kitchen). Obviously I will apply diversity to provide a suitably rated protective device & cable. However, I'm scratching my head on how to apply the diversity:
Is it:
1) Oven & hob total load in kw, then apply diversity = calculated load
OR
2) Apply diversity to the total load of each individually, then combine to calculate load
The OSG (table A2) refers to 10a + 30% fl of connected cooking appliances. So am I right in thinking it's 1?
Is it:
1) Oven & hob total load in kw, then apply diversity = calculated load
OR
2) Apply diversity to the total load of each individually, then combine to calculate load
The OSG (table A2) refers to 10a + 30% fl of connected cooking appliances. So am I right in thinking it's 1?