Discuss Are blue through crimps allowed on ring circuit. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
I'm a trainee electrician and I was working with a qualified electrician extending a 32A ring circuit and we were using 2.5mm single conductors (CPC was 2.5mm aswell) going through PVC conduit and then going through steel trucking.

And to connect the old ring conductors with the new extended ring conductors the electrician used blue through crimps to crimp the new and old conductors together in a small separate steel box connected to the steel trunking.

I said to him aren't you supposed to connect them together in some kind of juction box instead for a better strong connection and he said you don't need to.

So I was wondering if using blue crimps or just crimps in general to connect conductors together is ok and within the regs because I'm sure one of my college lecturer told me a few years ago that you can't do that.

I'm just curious is this allowed or not.

Thanks.
 
In theory crimps are great, and certainly are acceptable for maintenance free connections, extending earth bond wires, etc.

In practice though not all of them are suited to single strand wire (like 2.5mm T&E, for example), as mostly they are intended for stranded wire (both 7 strand like conduit wire, and finer like tri-rated or automotive wires).

So unless it is a crimp designed for the type of wire you are using, and properly crimped using the matching ratchet tool (or fancy hydraulic ones, etc), you would be far safer to use the likes of the Wago MF free box & terminals, checking carefully what it needs to be MF in practice (they often specify a cable tie as well as the clip-in lid, etc).
 
Crimps, properly fitted, make a very good connection.
Yes standard blue crimps are a good method of jointing stranded conductors, subject to being fitted correctly using the correct size crimp, correct tool etc (but that is true of any connection)

However most standard red/blue/yellow crimps are not suitable for solid core cable, such as 2.5mm T&E, this may be what your lecturer was referring too.

Crimping generally is the preferred method for connections once you get into the bigger sozes/higher current connections.
[automerge]1598472094[/automerge]
So unless it is a crimp designed for the type of wire you are using, and properly crimped using the matching ratchet tool (or fancy hydraulic ones, etc), you would be far safer to use the likes of the Wago MF free box & terminals, checking carefully what it needs to be MF in practice (they often specify a cable tie as well as the clip-in lid, etc).

How are do you suggest the OP mounts a wago box to the steel trunking?

I see no reason why a wago box would be better than a steel box mounted to steel trunking, I'd say it is a poor alternative.
 
How are do you suggest the OP mounts a wago box to the steel trunking?
Err, with screws through trunking to the wall holding trunking behind it, or nuts/bolts to top/bottom of trunking if accessible/preferred, same as you would mount a metal box?

I see no reason why a wago box would be better than a steel box mounted to steel trunking, I'd say it is a poor alternative.
Do you mean a joint box outside the trunking?

When I have done it the Wago box was comfortably smaller than the 50 x 100 trunking and fitted inside, has compartments to hold the Wago terminals, etc.
 
Err, with screws through trunking to the wall holding trunking behind it, or nuts/bolts to top/bottom of trunking if accessible/preferred, same as you would mount a metal box?


Do you mean a joint box outside the trunking?

When I have done it the Wago box was comfortably smaller than the 50 x 100 trunking and fitted inside, has compartments to hold the Wago terminals, etc.

Ok so you bolt the wago box to the trunking, but how do you get the cables into it? There no way to attach with a bush and lock ring.

Of course I mean outside the trunking, everyone knows you avoid joints inside trunking as far as possible. And you certainly never mount a box inside trunking!

Why on earth would you fit a joint box inside trunking? All that's going to do is really ---- off the next person trying to install a cable in the trunking!
 
In this scenario I'd much rather use Wago or Ideal 32amp rated push connectors within the galvanised box. No requirement whatsoever for it to be a 'maintenance free' assembly if it's accessible. I'm not keen on those red/blue/yellow through crimps as there are a lot of cheap rubbish versions out there.
 
In theory crimps are great, and certainly are acceptable for maintenance free connections, extending earth bond wires, etc.

In practice though not all of them are suited to single strand wire (like 2.5mm T&E, for example), as mostly they are intended for stranded wire (both 7 strand like conduit wire, and finer like tri-rated or automotive wires).

So unless it is a crimp designed for the type of wire you are using, and properly crimped using the matching ratchet tool (or fancy hydraulic ones, etc), you would be far safer to use the likes of the Wago MF free box & terminals, checking carefully what it needs to be MF in practice (they often specify a cable tie as well as the clip-in lid, etc).
Well the electrician did use proper blue through crimps and a sort of higher quality than standard crimp tool to crimp the conductors together. Its just I thought it just looked very unconventional. You could probably pull them apart if you used some force which would be much harder if the conductors were connected tightly using screws in a junction box.
 
In practice though not all of them are suited to single strand wire (like 2.5mm T&E, for example), as mostly they are intended for stranded wire (both 7 strand like conduit wire, and finer like tri-rated or automotive wires).

Agree entirely - it's a real bone of contention for me that they were included in 17th as an approved MF joint. There's too many variables in the style of tool available to crimp them, to the quality of the crimp itself. I mean you can go to Halfords and buy some blue crimps - but I wouldn't even use them on the car as the quality of those particular ones are so poor. I would argue that it could be easier for many to make a sound joint with a typical bakelite junction box than with a through crimp (particularly for people newer to the industry) - that said I haven't used a traditional unction box for years, I'm also a wago / Hager MF user - but even with wago, to actually properly comply with MF requirements requires some very specific rules to be followed (even down to the cable tie on the correct wagobox, and then you have the aggregate current bit) - I've seen many well versed electricians using wago as MF - but unbeknownst to themselves not actually in a fully compliant fashion - in short it's all far too complicated

Sorry got a bit off topic - yes fine if done properly but they're hard to do properly, especially in tight spaces and especially with single strand t&e. A place I used to work at extended old rings into dado with them as the proprietary connector - I'd say 50% of them failed at some point or another. A lot of the old skool swear by them though
 
Well the electrician did use proper blue through crimps and a sort of higher quality than standard crimp tool to crimp the conductors together. Its just I thought it just looked very unconventional. You could probably pull them apart if you used some force which would be much harder if the conductors were connected tightly using screws in a junction box.

Screwed connections are generally avoided for joints these days, Wago's or similar are generally the most popular with crimps also being compliant.
This is not to say there is anything particularly wrong with screw type connections, they are just becoming less popular
 
Agree entirely - it's a real bone of contention for me that they were included in 17th as an approved MF joint.

What would you replace crimped connections with in the regulations? Bearing in mind that crimped connections are the only realistic option for an MF joint in the majority of cable sizes, wagos don't go past 6mm!
[automerge]1598474026[/automerge]
Yeah sorry when I said steel box I mean't steel joint box. I just forgot the name

Usually it would be either an adaptable box or conduit box (aka BESA box)
 
Screwed connections are generally avoided for joints these days, Wago's or similar are generally the most popular with crimps also being compliant.
This is not to say there is anything particularly wrong with screw type connections, they are just becoming less popular
And using crimps I would say would increase resistance in the conductors. Therefore increasing the Zs readings.
 
And using crimps I would say would increase resistance in the conductors. Therefore increasing the Zs readings.

Only if the joint is made badly. A badly made joint of any kind will increase resistance and cause heating of the joint.
A skilled electrician will be able to make a good joint in conductors using the variety of methods available.

Screwed connectors can be prone to problems with stranded cables as the screw tends to spread the strands not properly clamping them, also the screw can cut through some strands.
 
Only if the joint is made badly. A badly made joint of any kind will increase resistance and cause heating of the joint.
A skilled electrician will be able to make a good joint in conductors using the variety of methods available.

Screwed connectors can be prone to problems with stranded cables as the screw tends to spread the strands not properly clamping them, also the screw can cut through some strands.
Ahh right makes sense
 
What would you replace crimped connections with in the regulations? Bearing in mind that crimped connections are the only realistic option for an MF joint in the majority of cable sizes, wagos don't go past 6mm!

Again it's an individual thing - but my point is that crimps mainly seem really suited to stranded cables and are available in such varying quality that there's a lot of room for error. I think this trend should have been realised when 17th was established by wider study. At that point an alternative could have been established - what it is, I don't know.
 
Ahh right makes sense
Again it's an individual thing - but my point is that crimps mainly seem really suited to stranded cables and are available in such varying quality that there's a lot of room for error. I think this trend should have been realised when 17th was established by wider study. At that point an alternative could have been established - what it is, I don't know.

Yes crimps are generally suited to stranded cable, and the vast majority of cables that we use are stranded.

The regulations require good workmanship an dpriper materials to be used, this addresses the use of poor quality materials or workmanship.

Exactly, there isn't a suitable alternative once you get out of the small sizes. For small sizes wagos and their equivalents are a suitable alternative.

Last week I had to joint a 25mm cable, I used through crimps because that's what was best suited to it as far as I am concerned. Soldering was not an option as it woukd take longer to get the hot works permit than do the job, shear bolt connectors would be too expensive and not so easy to insulate once connected.
 
Again it's an individual thing - but my point is that crimps mainly seem really suited to stranded cables and are available in such varying quality that there's a lot of room for error. I think this trend should have been realised when 17th was established by wider study. At that point an alternative could have been established - what it is, I don't know.
I'd like to say as well. I assume you wouldn't crimp stranded conductors and lay them directly inside steel trunking which has already got loads of other stranded conductors inside, as this would increase the chance of someone accidentally pulling apart a crimped conductor if they were pulling old conductors out for example. You would most definitely have to put the crimped conductors in a separate steel joint box.
 
Well the electrician did use proper blue through crimps and a sort of higher quality than standard crimp tool to crimp the conductors together. Its just I thought it just looked very unconventional. You could probably pull them apart if you used some force which would be much harder if the conductors were connected tightly using screws in a junction box.
I wouldn't like to think ANY crimp that I've ever installed could be pulled apart, physically. That's the idea of them...a permanent connection.
 
Yes crimps are generally suited to stranded cable, and the vast majority of cables that we use are stranded.

The regulations require good workmanship an dpriper materials to be used, this addresses the use of poor quality materials or workmanship.

Exactly, there isn't a suitable alternative once you get out of the small sizes. For small sizes wagos and their equivalents are a suitable alternative.

Last week I had to joint a 25mm cable, I used through crimps because that's what was best suited to it as far as I am concerned. Soldering was not an option as it woukd take longer to get the hot works permit than do the job, shear bolt connectors would be too expensive and not so easy to insulate once connected.
Did the 25mm through crimps have insulation around it or was it one of those crimps that don't have Insulation around it (such as all exposed metal) and/or did you incase the crimp joint in a joint box or junction box?
 
I'd like to say as well. I assume you wouldn't crimp stranded conductors and lay them directly inside steel trunking which has already got loads of other stranded conductors inside, as this would increase the chance of someone accidentally pulling apart a crimped conductor if they were pulling old conductors out for example. You would most definitely have to put the crimped conductors in a separate steel joint box.
....and that's absolute rubbish......crimp and heatshrink, no problem.
Generally you're talking about repairing damaged cables or mistakes installing, though. If you're jointing for a further cable, then always an external box. Available length dependant.
 
Last edited:
I'd like to say as well. I assume you wouldn't crimp stranded conductors and lay them directly inside steel trunking which has already got loads of other stranded conductors inside, as this would increase the chance of someone accidentally pulling apart a crimped conductor if they were pulling old conductors out for example. You would most definitely have to put the crimped conductors in a separate steel joint box.

If the conductors can be pulled out then the joint is bad.

Joints inside trunking are not ideal due to the damage it would cause if the joint does fail.
If a crimp joint has to be in trunking for any reason then I would insulate it with heat shrink.
 
Your bog standard red,yellow and blue insulated through crimps are for stranded cable and should not be used on solid as mentioned earlier, crimping solid requires a different crimping tool and crimp to make a sound reliable joint and if you have a ranger of crimping tools you'll tend to find solid cores are crimped with indent crimpers but there are exceptions that doesn't warrant a mention in this context.
Using the wrong crimp and crimper on a specific cable can and often will lead to deformed crimps thus a bad joint however tight it seems to be, one has to remember that other than the usual working load these connections need to tolerate they also need to withstand a possible 1000+ amps of fault current too.
 
with uninsulated crimp connectors, I'd expectto see heat shring sleeving applied over the crimp. sod fitting boxes. waste of effort . a joint of any description, if done properly with the right parts and the right tools, is a good joint.
 
with uninsulated crimp connectors, I'd expectto see heat shring sleeving applied over the crimp. sod fitting boxes. waste of effort . a joint of any description, if done properly with the right parts and the right tools, is a good joint.
Fair enough that actually makes sense now with the heatshrink. My bad. I dont have so much experience in the electrical Industry as I'm still a trainee. :)
 
with uninsulated crimp connectors, I'd expectto see heat shring sleeving applied over the crimp. sod fitting boxes. waste of effort . a joint of any description, if done properly with the right parts and the right tools, is a good joint.
Nice heat gun though, tel.......that cig lighter's not up to it nowadays.;)
 
Collecting some comments from above:

Joints correctly and skilfully made using proper materials appropriate for the application, are good joints. It matters not whether they are Wagos, screw terminals, inline crimps, crimped lugs on a stud, soldering or whatever, unless you have to meet a specific standard that is more prescriptive (e.g. for ATEX or MF situations). As Davesparks points out (and I regularly point out to anyone who will listen) a good electrician can make a sound joint with any suitable material. Making connections is one of the most fundamental skills an electrician can have, which used to be taught in great detail but now seems to have fallen by the wayside. But it is a skill, not just a list of do's and dont's like: 'Blue crimps are OK for RFC's.'

There are many bad / unsuitable materials and unskilled persons out there. The dodgy insulated crimps from the car shop, the guy who has good crimps but uses a duff crimp tool, the numpty who crimps them with pliers and his mate who uses stranded-only crimps on solid conductors. The regs don't call these out specifically, because there is the overall requirement for proper workmanship and materials which covers it.

Crimping, using good materials correctly installed, is reliable and secure. If a cable can be pulled out of a normal crimp without damaging / stretching the rest of the cable, it wasn't properly installed. If I crimp a ring to a 2.5mm² tri-rated, put the ring in the vice and pull, the cable rips apart leaving strands still stuck in the terminal. Any good connection will not add measurable resistance, otherwise if it carries more than a whiff of current, it will overheat. A connection that does not overheat is not however automatically to be considered a good one, as it might fail with time or movement in a way that it should not.

Additional insulation (and sometimes even basic insulation) is sometimes required to complete a joint or make it suitable for the installation conditions. Heatshrink of the right type is a versatile material for many kinds of joint. Applying insulation requires skill and knowledge to ensure that it is adequate, e.g. of the same strength and durability as cable insulation. Just putting any random kind of heatshrink over an uninsulated crimp is not in itself adequate.

Personally, I'm not too fussed about properly made inline joints with suitably robust insulation lying within trunking. If there are many joints, or the trunking is very busy, or there is a reason for them to be vulnerable, then a terminal box is needed. Bare blue butt crimps are not quite up to the mark.

Perhaps I should run a course. 'From blue butts to bellhangers in 10 easy lessons.'
 

Reply to Are blue through crimps allowed on ring circuit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I'm in the process of renovating a house. As I go through room by room I am removing old plaster and as the cables are exposed at this point I...
Replies
14
Views
4K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
20
Views
2K
Hello, I am renovating a house. I am rewiring myself. I am getting an electrician to install a new consumer unit & test all my work. I'm looking...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock