Discuss Are mains sockets permitted in bathrooms? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Pity!
As I said above. You cannot leave live cables in the wall and just plaster over them, unless they are at least 50mm from the surface.

So you have two obvious options
1. Rewire the socket so there are no cables in the wall. This may be tough as the cables come from two directions, but there may be a service duct in a corner, or other routes that the cables could take. You'll obviously need to find a location for a junction, or two.
2. Connect the conductors together, in the existing back box, using some insulated terminal block, or Wago-type connector.
Then put a blank plate over the back box, but on top of your new plasterboard so it can be seen.
 
Sounds like it's an upstairs RFC feeding sockets below and a single T&E drop.

Not a 70's built house by any chance?
 
Pity!
As I said above. You cannot leave live cables in the wall and just plaster over them, unless they are at least 50mm from the surface.

So you have two obvious options
1. Rewire the socket so there are no cables in the wall. This may be tough as the cables come from two directions, but there may be a service duct in a corner, or other routes that the cables could take. You'll obviously need to find a location for a junction, or two.
2. Connect the conductors together, in the existing back box, using some insulated terminal block, or Wago-type connector.
Then put a blank plate over the back box, but on top of your new plasterboard so it can be seen.
Yes, that's the route I'll take terminal block with a wall plate.
 
Yes, that's the route I'll take terminal block with a wall plate.
Use Wago or similar, not those horrible choc block things...

This may look expensive on the face of it however they will cover most options in your house and are rated for up to 32 amps: https://www.NoLinkingToThis/p/wago-lever-connector-set-32a-85-pieces/2305r
 
Erm...what sauce would you like on your hat, MDJ?
I installed a new loo and got a Building Warrant and Completion Certificate for that.
The lady from BC who inspected it was in the house less than 1 minute, said "Nice shower!" and left!
 
Erm...what sauce would you like on your hat, MDJ?
I installed a new loo and got a Building Warrant and Completion Certificate for that.
The lady from BC who inspected it was in the house less than 1 minute, said "Nice shower!" and left!
Well there is always one t!t
 
'Thank you for your quick reply. The socket is too close to zone 1. Behind the socket three cables converge, bearing in mind that I am replacing the plasterboard in that area what is the best method of connect the cables together?'

Either use the existing back box, suitable connectors and a front plate or a suitable maintenance free junction box. Any further information, would be a step by step guide, which is against forum rules.

I'd consider employing a competent electrician. Such work could be notifiable to local building control.
You can build a cupboard around the socket
 
Use Wago or similar, not those horrible choc block things...

This may look expensive on the face of it however they will cover most options in your house and are rated for up to 32 amps: https://www.NoLinkingToThis/p/wago-lever-connector-set-32a-85-pieces/2305r
Thanks for the suggestion, I've ordered a box they're just what I need.
 
Use Wago or similar, not those horrible choc block things...

This may look expensive on the face of it however they will cover most options in your house and are rated for up to 32 amps: https://www.NoLinkingToThis/p/wago-lever-connector-set-32a-85-pieces/2305r
Thanks for the suggestion, I've ordered a box they're just what I need.
 
I would suggest you get an Electrician in ;)
 
Some places find that sockets in the bathroom are the way to go...
WP_20180824_08_11_04_Pro.jpg
Obviously the low level socket is nearly 15cm from the edge of the wash basin, ideal for my straighteners, and the higher level hairdryer and shaver socket make sense too as they are miles away from the basin...
 
and while I am talking Spanish electrics,
WP_20180824_08_10_36_Pro.jpg
as a total amateur, what are the 3 chaps at the right? I am guessing they are to do with the card-switch system, so when you put your card in the slot so you can use the lights etc these activate the circuits for them and the sockets and aircon? Clearly that wee slotty thing can't carry the load on its own. Or am I talking rubbish...
 
Some places find that sockets in the bathroom are the way to go...
View attachment 43928
Obviously the low level socket is nearly 15cm from the edge of the wash basin, ideal for my straighteners, and the higher level hairdryer and shaver socket make sense too as they are miles away from the basin...
Bleedin' 'ell...….Johnny Depp talkin'?
 

Reply to Are mains sockets permitted in bathrooms? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
610
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
I have a socket in by bathroom vanity unit, .75m away from the edge of the bath. The vanity is completely enclosed with a sink on top and doors...
Replies
23
Views
2K
Had to remove a led strip from a bathroom today because it’s getting tiled, now the led strip that was there was low voltage but didn’t have...
Replies
10
Views
930
Hello all, I need to have an electric car charger installed but at the moment I'm puzzled about what my options are. My garage is at the back of...
Replies
4
Views
661

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock