Discuss Are these earth wires connected to neutral? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I found a picture online of a standard UK connection in a block of flats.

Where I have circled blue, would those earth clamps around the orange cable somehow cut into the neutral wire to connect within the orange sleeving?

Or are they just clamped to the sleeve for some arbitrary reason?

earth neutral.jpg
 
That is not in any way a standard connection in a block of flats.

Those clamps are not arbitrary, they are connected to the metal sheath of the cable which is the earth conductor for that type of cable. This cable is called MICC, commonly known as 'Pyro'.
However the use of earth clamps in this manner is not technically correct.
 
No, there is no connection to neutral at those clamps.

The cable is mineral insulated copper sheathed, with an orange PVC oversheath. The copper sheath is what gives the cable its overall form and strength and served as the CPC of the cable, but it isn't visible in the pic because it's covered by the orange PVC oversheath. Cuts have been made through the PVC to allow the clamps to connect to the copper sheath. Inside the sheath, the solid copper line and neutral conductors are insulated with magnesium oxide powder, which is sealed at the ends to prevent moisture ingress.

However, this picture shows very bad installation practice. MICC should not be installed and terminated in this way. The glands at the top of the cables should be mounted into an earthed metal enclosure which would make the connection to the sheath and enclose the tails emerging from the seals, which have only basic insulation and should not be exposed. It would also support the cables and prevent them hanging from the conductors as they are seen doing here. The concentric cables connected to the top of the cutouts are shoddily installed too.

In a nutshell, don't learn anything from this one.
 

Reply to Are these earth wires connected to neutral? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
726
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
556
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
700
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
581

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock