Discuss ariston water heater install in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
hi ,ive been asked to install an ariston tankless water heater ,the manual states its 9.5kw at 240v with min cable size of 6mm and that it will pull 39.6 amps .the cable run is 17 meters partly enclosed in an under concrete floor pipe along with 3 other 2.5mm cable runs and the rest of the run back to the board is clipped direct ,there is currently no mcb available to use and no rcd protection either .
my questions are > is 6mm good enough
can i use a 40A mcb with no rcd
should i install a seperate CU which would have 63A rcd and 40A mcb
many thanks for any advice
john
 
The manual said 9.5kw at 240v, drawing 39.6amps but worth remembering that it only draws 39.6 amps if you have an exactly 240v supply.
As a silly and extreme example if you actually had the UK minimum permitted voltage (230v - 6%) and had 5v further volt drop over 17m of 6mm T+E it's now pulling 45 amps. Unlikely of course.

10mm csa cable would permit a higher value MCB and suffer less volt drop, and as above be more suitable in the first place.
 
+1 for 10mm in a case like this.

Even if 6mm would do, it leaves no future options for replacement/upgrades. If a new floor has gone down and they need to replace the heater in 10 years they'll be thankful they paid the very slight extra for 10mm.

It might mean a larger conduit too of course, but still worth it when there's any doubt.
 
+1 for 10mm in a case like this.

Even if 6mm would do, it leaves no future options for replacement/upgrades. If a new floor has gone down and they need to replace the heater in 10 years they'll be thankful they paid the very slight extra for 10mm.

It might mean a larger conduit too of course, but still worth it when there's any doubt.
thankyou for the reply ,i had thought 10mm was probably better option ,the floor is not new and is concrete the pipework it will be run in was put in years ago by the aircon guys to get from the cellar to first floor its actually a 6" pipe and theres no chance of potential upgrades or changes to the heater in future ,all i have to do now is find a suitable mcb/rcd combination to install .FYI i can run another set of tails from the henley block to a seperate cu
 
The manual said 9.5kw at 240v, drawing 39.6amps but worth remembering that it only draws 39.6 amps if you have an exactly 240v supply.
As a silly and extreme example if you actually had the UK minimum permitted voltage (230v - 6%) and had 5v further volt drop over 17m of 6mm T+E it's now pulling 45 amps. Unlikely of course.

10mm csa cable would permit a higher value MCB and suffer less volt drop, and as above be more suitable in the first place.
thankyou for the reply ,i had thought 10mm was probably better option ,the floor is not new and is concrete the pipework it will be run in was put in years ago by the aircon guys to get from the cellar to first floor its actually a 6" pipe and theres no chance of potential upgrades or changes to the heater in future ,all i have to do now is find a suitable mcb/rcd combination to install .FYI i can run another set of tails from the henley block to a seperate cu
 
Judging from the details you have provided I would say 10mm would be more suited rather than 6mm. I would fit an RCD also.
thankyou for the reply ,i had thought 10mm was probably better option ,the floor is not new and is concrete the pipework it will be run in was put in years ago by the aircon guys to get from the cellar to first floor its actually a 6" pipe and theres no chance of potential upgrades or changes to the heater in future ,all i have to do now is find a suitable mcb/rcd combination to install .FYI i can run another set of tails from the henley block to a seperate cu
 
thankyou for the reply ,i had thought 10mm was probably better option ,the floor is not new and is concrete the pipework it will be run in was put in years ago by the aircon guys to get from the cellar to first floor its actually a 6" pipe and theres no chance of potential upgrades or changes to the heater in future ,all i have to do now is find a suitable mcb/rcd combination to install .FYI i can run another set of tails from the henley block to a seperate cu
If going with a separate CU then any of the "shower" units should do fine - 63A RCD and 40 or 45A MCB.

You'll want one with a good amount of space in it to nicely terminate 10mm, but the current metal ones do tend to have more space in now than they used to.

It might pay to get a 2 or 3 way one with blanks to give you the extra space (and the possibility of adding maybe a 6A or 16A in the future.
 

Reply to ariston water heater install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
We own a small, one bedroom flat (built 1989). An EICR inspection raised three C2 observations and recommendations: (A) The shower cable, and...
Replies
8
Views
4K
Hi folks. I'm asking so that I can do some planning, and then hire a local electrician to do the work. WHAT: This is my first question, ever...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock