Discuss Armourd cable clipped direct will the sun uv affect the cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

A

AA410

Hi all i have a customer that wants a supply to an outbuilding clipped direct to a brick wall looks to be the best route but the cable will be in full sun will this have much of an affect to the cable advice please
 
The outer sheath on SWA cable is UV stabilised PVC so it can be installed in direct sunlight. If it's running surface on an outbuilding you might still want to install steel capping over it for other reasons such as preventing physical damage from vehicles and theft etc.
 
Last edited:
Yes it will have an effect, it will eventually break down under the UV radiation.
Cables suitable for use outside will have a black sheath which is more UV stable than other cable sheaths so it will survive a lot longer, but ultimately it will go at some point in time.
 
Thanks for your help it is black pvc steel wire Armored cable as i understand it will go grey in time as far as the ambient temp it will be around 25 deg
 
Yes it will have an effect, it will eventually break down under the UV radiation.
Cables suitable for use outside will have a black sheath which is more UV stable than other cable sheaths so it will survive a lot longer, but ultimately it will go at some point in time.

I've seen 30/40 year old SWA's exposed direct with little degragation... think the swa will probably have a longer lifespan than any installer on the UV concern..
 
I'm over here in Saudi up over 2000 ft above sea level, where the temp is 50+ in the summer and UV values off the scale, they don't do a sun cream with enough protection, and I've seen SWA, that is over 20 yrs old and perfect.
 
The wages must be good at that temp it must be like standing in an oven

If you can imagine coming out of a AC office/car it is literally like walking into someone holding an hair dryer and pointing it at you the whole time.

Ha Ha Ris I hav a photo I'm sure you seen it of a poster that has a old fashioned mercury thermometer with a huge 6" nail hammered into the scale at 49c, labelled SA HSE
 
If you can imagine coming out of a AC office/car it is literally like walking into someone holding an hair dryer and pointing it at you the whole time.

Ha Ha Ris I hav a photo I'm sure you seen it of a poster that has a old fashioned mercury thermometer with a huge 6" nail hammered into the scale at 49c, labelled SA HSE
don't forget the burning hands etc on the steering wheel and the seat belts etc.

the most miserable ive been was in turkey at the airport and there ac was broken, now that was hot
 
If it's a dry heat you can live with it and get used to it. Humidity and heat together is the killer for me, I just spend the day dripping in sweat.
 
Sounds like Durban, it's as humid as a ------ armpit. Cape town gets hot but mostly without the high humidity thankfully.
 

Reply to Armourd cable clipped direct will the sun uv affect the cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

This might come across as a really daft question to people who work with cable tray quite often but as part of my AM2, I am to clip FP200 to the...
Replies
31
Views
2K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
916
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
668
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
741
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
624

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock