Discuss Aurora 3.0 inverter on a 3.84kw system - is this reasonable? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

U

upnorth01

I had a solar panel installation completed this week. There are 16 x Csun 240-60P panels (3.84kw capacity, on a SW facing roof in north-east Scotland) and a power-one Aurora PVI-3.0-OUTD inverter. From the inverter booklet I see this has a max recommended DC power in of 3.5kw and max AC power out of 3.3kw. It seems from my reading of the sepcification that this is too small a unit and the system should have been fitted with a PVI-3.6 model. I guess I have 3 questions - is this system within a reasonable tolerance or does the inverter need to be changed, what will happen when the panels deliver more power than the inverter can cope with (damage the inverter / output stops altogether / output continues subject to the maximum cap of what the inverter can process etc) and will running near full capacity reduce the life of the inverter.

Any help or comments will be appreciated. I have found the forum most helpful. Thank you.
 
Last edited by a moderator:
Re: Aurora 3.0 inverter on a 3.68kw system - is this reasonable?

16 x 240 = 3840. Are you sure it is 3.68?

- The inverter is undersized. The correct Aurora model would be the PVI-3.6-OUTD (use the UK version limited to 16A).
- The inverter will only draw from the panels what it can deal with so no damage will be done provided the string(s) have been wired so that input voltages are within tolerance.
- Running at full power all the time will reduce the life of the inverter.
- You will lose some of the annual production because of limiting.
 
Bruce,

Oops - indeed it is 3.84 - got the figures mixed - edited my post to correct. Thank you for the information - its not as bad as I feared (not dangerous and production continues rather than just stops) but I will try and persuade the installer to replace. I suspect this will be met with some opposition. Would MCS take up a case like this, and if so is it likely to yield any results?
 
Last edited by a moderator:
Re: Aurora 3.0 inverter on a 3.86kw system - is this reasonable?

3.84

It is a pretty clear mistake if all is as you have presented it and the installer should be willing to fix it. You will have to go through their complaints process before any of the supervising bodies will get involved.
 

Reply to Aurora 3.0 inverter on a 3.84kw system - is this reasonable? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K
Good Morning All! Always appreciate reading the great ideas and conversations in the forums, and now actually have a chance to ask a question...
Replies
0
Views
876
Hi new member here looking for advice. I’m having a nightmare with my installer and Solis and wondering if anyone can come back with any ideas...
Replies
50
Views
11K
Hi guys, I am new to the forum so be nice! I used to install solar PV systems back when the tariffs were still good, and I've never had to go...
Replies
5
Views
5K
My system has had an intermittent problem for the last few months. The inverter has occasionally been reporting PV Voltage Too High, then it would...
Replies
13
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock