To protect human life.

It's not about limiting the current to 30mA but ensuring that it operates if 30mA is passing through - well actually 150mA for additional protection to operate within 40mS.
But if the result is an instant huge fault current that starts way above that figure why have it, hence my argument that the fault current grows from zero and fast.. In milliseconds; but is nipped in the bud by the RCD before it gets the chance. Plus if your argument is true why doesn't a 500mA protect you.
 
Last edited:
30mA RCDs are designed to trip when they detect earth leakage greater than 30mA.
Most will trip below this figure.
So if an RCD detects an earth fault current of 4600A, it will trip, and it will trip within 40ms.
An MCB will also trip if it detects a fault current of 4600A, though it is more likely to trip instantaneously or within 10ms.
Where RCDs are good, is that they will trip at lower currents which an MCB might not trip at, or may take seconds, minutes, hours or even days to trip.

So no, RCDs do not limit fault current, just as fuses and MCBs don’t limit fault current.
 
Explain the fault curve on a fuse chart if earth fault current doesn't grow with time. It shows how long it takes the fault to grow to a large enough magnitude to rupture the fuse. An RCD gets that curve chopped early. But by a means of imbalance measured via earth leakage
 
Last edited:
Well I would like to know the science behind how it saves your life if it doesn't limit the current your body receives
Imagine you’re outside mowing your lawn with your hover mower.
The grass is damp, the cable is damp, you accidentally cut through the cable.
You make the mistake of picking up the damp live part of the cable.
You get a belt, you fall down and are unable to release the cable.
Because there’s no CPC in the cable and you’re outside, the fault path is via the general mass of the earth, which in your garden has a high resistance. So high in fact, that there is not enough current to cause the MCB to trip.
You manage to hang on to life for 20 mins, unfortunately it takes your partner 30 mins to wonder what you’re doing and come looking for you.
If there had been a working RCD, the power would have been cut off in 40ms, you’d have got a belt and your arm might ache for the rest of the day.
 
I was lucky once, or maybe I was sensible?
I borrowed a hover mower from a relative to mow my lawn.
I did not cut through the cable, but someone else had and made a botched repair.
I finished mowing, unplugged the cable near the mower and started winding the cable round my arm, walking back towards the socket in my out house.
The cable was damp and as I got near to the botched repair I got a belt.
Fortunately, the RCD socket I had installed in the out house tripped, though the one in the CU did not.

You’re not supposed to have RCDs in series, but I installed the socket before the CU was upgraded by the Council.
The difference between an RCD plug or socket and an RCD in a CU, is that every time the plug or socket is used, they are quite likely to be tested.
Whereas no one bothers testing the RCD in the CU.
Who wants the hassle of resetting the video, TV, stereo, cooker, etc.
 
Well I would like to know the science behind how it saves your life if it doesn't limit the current your body receives
..Only any good with 230-250V AC. to earth
It limits the time the shock is received for (if it works !-Not sticking)
, and you restrict the current (unless covered on Copper mesh !)
So you don't get one of those "gargling moment's" !
 
30mA RCDs are designed to trip when they detect earth leakage greater than 30mA.
Most will trip below this figure.
So if an RCD detects an earth fault current of 4600A, it will trip, and it will trip within 40ms.
An MCB will also trip if it detects a fault current of 4600A, though it is more likely to trip instantaneously or within 10ms.
Where RCDs are good, is that they will trip at lower currents which an MCB might not trip at, or may take seconds, minutes, hours or even days to trip.

So no, RCDs do not limit fault current, just as fuses and MCBs don’t limit fault current.
Rcds are advertised to operate at 30ma but they are actually manufactured to function at 27 to 28ma. Manufacturers hedging their bets on that one:D
 
  1. Preventing a current passing through the body of any person or any livestock
  2. Limiting the current which can pass through a body to a non-hazardous value
An RCD functions to disconnect before most fatal events occur in accordance with the below graph, the disconnection time is such that the human body should be able to withstand the expected fault current flowing through the body for that duration without death, but not without pain and reaction, in most cases.
To prevent a current flowing or to limit the current to a non hazardous value would be achieved by non conducting locations, SELV or electrical separation. However the primary means of preventing a current is to make sure that conductors are not accessible to touch in the first place.
Shock physiological time mA.jpg
 

Reply to Automatic disconnection of supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Cathodic Protection Station with Switching Power Supply for Buried Metal Structures Benefits of the Switchmode Cathodic Protection Rectifier...
Replies
1
Views
479
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock