For I2C : My Dilog AVI has an 18K input impedance. High enough normally of course (if no other leakages), but too low for it to be driven anywhere close to 230V by a Martindale proving unit (which can only drive about 3mA, - hence about 60V on testing the AVI).
 
i reallyneed to check the input impudence of my AVO 8.i forgot what it was back in 1982.
 
I find it hard to believe,that several electricians suggest the test described,by the OP...one numb one...but plural?

The fundamental requirements,are to both understand how the test equipment functions,and how to use it,to discover whether safe or not.

Experience of the various scenarios,where line voltage can occur,would make ALL the necessary combinations of testing,second nature.

Line/neutral reversed,a live neutral,live earth,or all live...are all possible or probable occurrences,and all testing should indicate such.

The gentlemen advising otherwise,have possibly never inspected a connected burger bar,by first putting one probe on the yard surface,and the other on it's brightwork :)
 
If you're testing for isolation it should be isolated. If so, why worry about an rcd tripping.
It should all be dead, so test it all.
Fault finding may be different.....but it should have tripped, anyway.
 
Just an appendage,to my previous post,which mentioned correct understanding of a test instrument,would be to remember that an AVI is not only used to check for safe isolation.

It is as handy,though not it's primary use regarding this conversation,for proving a voltage present.

A quality AVI,with maybe resistance and DC capability,can be a fine,compact troubleshooting device.

I have an old TPT220,which stays in the glove box,or hand luggage...and it's paid for itself a hundred times over:)
 

Reply to AVI (Approved Voltage Indicator) - Common Misconceptions in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
1K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
965
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock