Can't see need for earth link. We use large industrial back up gens all the time and never do this . Just need to know what Ze is when DNO earth is available and what Ze is on your local spike. Then make sure installation works for both scenarios. Generators should have the earth neutral bond in place at manufacture, although you need to check otherwise the earth rod does nothing.

As a matter of discussion, if you are worried about no DNO earth during a power cut, how do you know you have the earth back when the power comes back on?
 
Can't see the point of that set up at all, the link between main and standby, unless physically removed each time you go onto generator supply. But if that's what you want to do, then surely better to use use a 3 pole C/O switch for a single phase set-up.

But what do i do with a 3 phase set-up, which is what i deal with?? That would need a 5 pole C/O switch or a 4 pole with a linked Aux contacts linked SP contactor (4 pole + E)..... Never done so, and i can't see myself ever doing so either!! So tell me what i'm doing wrong??
 
The only 3Ph backup generators I’ve dealt with were on private 11KV networks.
Basically we didn’t have to worry about exporting the earth as any work on the system was under our control. The incoming to the intake was at either 11 or 33KV on OH lines so as regards earthing arrangements we were independent.

Out of interest E54, if you have more than one DG set what do you do about the star point earthing of your setup?

As for the reason I mentioned the link, it was in a UKPN document sent to me when I got involved in installing a LV generator. They seemed a bit worried about their staff getting fried.
 
Out of interest E54, if you have more than one DG set what do you do about the star point earthing of your setup?

Not really a problem Tony, at least not from my standpoint as our gensets come ordered as matched pairs with the same winding pitch, so both sets can have paralleled neutral point earthing.

Normally more of a problem with gensets with differing winding pitches, in that case a reactor can be included in the commoned neutral, there are other methods that can also be used...
 
This is why I asked. We used automatic earth transfer switching to the common earth bus. The bus grounded via a NER.

Ah, i should have realised you were talking about MV, yes we use NER's on MV gensets, even on single units, to reduce the available fault current...
 
Whats a NER?

Im curious after what happened today.

Do you normally use buz bar changeover switches usinh castel keys?

Is this more an industrial application or common?

NER = Neutral Earthing Resistor!!

I rarely use castel key's on our installations as they are all fully automatic, on both the MV and the LV Switchboards, as i tend to work on large hospital installations. Only ever use them on the downstream MV side, when distribution is via RMU's....

And yes, you could say this is found more within the Larger commercial and industrial sectors...

Tony has used mechanical castell and other interlock key system far more than myself
 
Shanky, It’s mainly industrial. Unlike E54’s systems ours were all manual switches.

A typical situation would be two incoming supplies and a bus section switch.
Three locks, two keys. This would give you three options:
Supply A & B CLOSED bus section switch OPEN
Supply A CLOSED bus section switch CLOSED Supply B OPEN
Supply B CLOSED bus section switch CLOSED Supply A OPEN
You can’t parallel supply A & B

There are ways around this. I have a couple of Castell master keys. These were kept locked away at all times and never left my sight.
I just know E54 will shout at me for this.
 
Last edited by a moderator:
Shanky, It’s mainly industrial. Unlike E54’s systems ours were all manual switches.

A typical situation would be two incoming supplies and a bus section switch.
Three locks, two keys. This would give you three options:
Supply A & B CLOSED bus section switch OPEN
Supply A CLOSED bus section switch CLOSED Supply B OPEN
Supply B CLOSED bus section switch CLOSED Supply A OPEN
You can’t parallel supply A & B

There are ways around this. I have a couple of Castell master keys. These were kept locked away at all times and never left my sight.
I just know E54 will shout at me for this.

No not at all, they are in the hands of someone that KNOWS what they are doing!!
 
No not at all, they are in the hands of someone that KNOWS what they are doing!!

You shouted at me for paralleling two 1600KVA transformers and exceeding the boards maximum fault current.
Two guys working together, one on the each ACB. It will take me longer to type “OPEN” “CLOSE” than it took for the switches to operate. We would have been damned unlucky for a fault to occur in that split second. I did take the precaution of putting the 11KV on to one feeder, that needed my 2[SUP]nd[/SUP] naughty key.
CastelPreciphouse_zps49b2d78a.jpg

Normal operation A, B, D, E closed C & F open.
 
Standing instruction is to never potentially over stress equipment, even for switching time, except in exceptional circumstances that are fully risk assessed and appropriate action taken. This would certainly include preventing any access to switch gear etc

how did you know you had exceeded the boards max fault current in your example? You can't just add the fault currents together!
 

Reply to Back up generator on domestic in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just a query. As people have been asking me about changeover switches and generators. If a domestic house already has PV solar, and customer...
Replies
9
Views
2K
My house had previously been wired for a generator (probably not by code to this day) but previous homeowner disconnected and instead hooked up...
Replies
1
Views
529
Hi All Had an enquiry about installing a generator fed UPS to a house. I have a minimal amount of experience with UPS but am certainly no expert...
Replies
3
Views
1K
A customer has asked me to install a generator to supply her house for when they have a power cut. I have already said this is beyond my...
Replies
13
Views
6K
I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock