Discuss best method to go with in the UK Electrical Forum area at ElectriciansForums.net

G

glasgospark

3 phase supply into house
full house off the red phase
but we have a 3 phase ground source heat pump
i have terminated into 100a lucy blocks N l1 l2 l3 from the distributors 3pn isolator

was thinking of a 3p 32a type c breaker in its own enclosure to feed the heat pump
 
sorry to be vague , but i have all that side of it configured , was a question on the fact i need the heat system on its on 3 phase circuit as the house is off the L1 basically best method to do so ,
as stated before i was thinking of a encloser to hold the type c 3 phase breaker
 
I agree with Handy, and to add, the heat source pumps I have installed are usually 2kw max per phase for domestic use so a 32 amp TP&N supply would be too big unless you install cable too large, you may find a 10 amp supply enough for a 3 phase pump.
 
I agree with Handy, and to add, the heat source pumps I have installed are usually 2kw max per phase for domestic use so a 32 amp TP&N supply would be too big unless you install cable too large, you may find a 10 amp supply enough for a 3 phase pump.

actually agreed mdj , but the install is being carried out by a 3rd party , the pump is pulling 6a max per phase all i was told and asked to provide was a 3phase 32a rotary isolator
 
actually agreed mdj , but the install is being carried out by a 3rd party , the pump is pulling 6a max per phase all i was told and asked to provide was a 3phase 32a rotary isolator
well then supply a 3 phase rotary isolator for them, single phase pumps do usually need a 32 amp supply, if it is 3 phase though I would supply a 10 amp c rated supply to the 32 amp rotary isolator, how far away is the pump from the House? you may find a 4mm2 more that enough if not far away.
 
well then supply a 3 phase rotary isolator for them, single phase pumps do usually need a 32 amp supply, if it is 3 phase though I would supply a 10 amp c rated supply to the 32 amp rotary isolator, how far away is the pump from the House? you may find a 4mm2 more that enough if not far away.

the full system is in the garage about 3 meters adjacent to the main board they asked for 10mm :O but i settled at 6mm ,
do you think the method proposed above is ok coming off the distributors lucy blocks into the type c breaker to feed the rotary
 
Can't see any reason why not, providing you protect the circuit with an appropriate protective device and isolation there should not be a problem. I would double check their requirements though, I mean you could run a 10kw shower off a 10mm2 cable let alone a 6 amp supply to a pump. the hiccup could be the earthing arrangement, I would use the houses and Rollocks to TT, avoid an RCD at all costs IMO for a pump which is related to the heating system. (Tin Hat on)
 

Reply to best method to go with in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
573
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Replies
2
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock