Search the forum,

Discuss Best type of lighting in stables in the UK Electrical Forum area at ElectriciansForums.net

stables come under the broader classification of agriculural and horticultural. just because the BS does not specifically mention stables per se.
polo mints are not advertised as containing a nitrogen/oxygen mixture, but we all know there's a hole in the middle, same as with your thinking.
 
So far only DPG had spoken any sense. Anyway, this time next week I will have my stables safely wired and connected to the mains. Certainly upset a few folk on here! Anyway, I'll agree to differ on the facts. I know I'm right, even if I'm not (and I am) so what? Life's too short to worry about details.
 
It's a bizarre concept that farms, farm buildings, cow sheds, chicken sheds, outbuildings should all be covered by the wiring regs, but for some reason stables specifically are excluded? Why on earth would you think that would makes sense?
 
It's a bizarre concept that farms, farm buildings, cow sheds, chicken sheds, outbuildings should all be covered by the wiring regs, but for some reason stables specifically are excluded? Why on earth would you think that would makes sense?
 
Enjoyed the argument though - always good to have a good debate.
 
Still can't see stables mentioned, it's not commercial and it's not agricultural.

View attachment 38544

You can quite clearly see from the picture that you have provided that your earlier assertion that BS7671 applies only to dwellings is complete twaddle.

This should be enough evidence to consider that your understanding of the wiring regulations may not be as good as you thought. Certainly enough to consider wiring to the requirements of section 705.
 
bet with OP's disregard for rules and regulations, he's got Shergar hidden away in them stables. :eek:
 
You cannot assume that because stables aren't mentioned that they are included under some other heading. I get the point about livestock protection, but we don't have livestock only horses. The planning officer said if the building is not normally occupied, as in a dwelling, office, factory etc then BS7671 doesn't apply. Sorry to keep repeating myself, it is not commercial, not agricultural and we don't keep livestock.
 
Crazy argument. Stable next to a house needs to comply with regs, animals on a farm same, but your stable doesn't need to comply with any wiring regs at all. Yep, right.
So by your argument you could wire it all in bell wire and you are not contravening any regulations?
 
Google 'are horses livestock'. I have just come off the phone to my local planning officer. He has confirmed if the stable is on its own land, on it's own supply, and is not normally occupied then BS7671 does not apply.
 

Reply to Best type of lighting in stables in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top