Discuss Best way to check continuity of cpc for lighting in the Lighting Forum area at ElectriciansForums.net

Reaction score
3
20 y old lighting circuit with cpc at the board but terminating into class 2 recessed down light fittings. Looks like there is a junction box in the ceiling void feeding the light with L&N but I can't access the junction box so not sure how can prove continuity of the circuit?
 
in reality. if they are all class 2 lights, the obvious danger points are the switches if they are conductive.

i would start by checking there.
 
Can you put in a “shower” or “garage” board with rcd dedicated just for the new shower and not touch the existing circuits as they are?

changing the board involves as much testing as an EICR anyway
 
I’ve been known to try a B6 rcbo connected to a plug top, plugged into the sockets circuit, and wago the lighting circuit to it as a quick sanity check that nothing will cause instant tripping. Not desperately safe of course but proves the point.
Sometimes you can het a clamp meter around L and N which is a safer test.

Apart from that I’d crack on - do the other circuit and then IR tests (L+N to cpc bar)

(I think BPG1 covers this situation of a cu change with no cpc on lighting btw.)
 
I’ve been known to try a B6 rcbo connected to a plug top, plugged into the sockets circuit, and wago the lighting circuit to it as a quick sanity check that nothing will cause instant tripping. Not desperately safe of course but proves the point.
Sometimes you can het a clamp meter around L and N which is a safer test.

Apart from that I’d crack on - do the other circuit and then IR tests (L+N to cpc bar)

(I think BPG1 covers this situation of a cu change with no cpc on lighting btw.)
Thanks, there is a cpc at the CU just cannot find where it terminates at a particular class 2 lamp on the circuit as Junction box feeding it is inaccessible so guess i will just have to rely on where I can check it elsewhere on the circuit
 
I wouldn’t waste too long on it - my main concern would be whether it will cause me grief once reconnected.
Regarding the paperwork you can’t get an R2 or Zs so you’ll have to add a note to that effect, and you are adding RCD protection which will serve as last resort fault protection in absence of verifiable fault protection via CPC.
(Obviously I’d be recommending lighting is rewire in due course too.)
 
I wouldn’t waste too long on it - my main concern would be whether it will cause me grief once reconnected.
Regarding the paperwork you can’t get an R2 or Zs so you’ll have to add a note to that effect, and you are adding RCD protection which will serve as last resort fault protection in absence of verifiable fault protection via CPC.
(Obviously I’d be recommending lighting is rewire in due course too.)
Thanks for your comments- makes sense
 

Reply to Best way to check continuity of cpc for lighting in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
867
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi all. Reasonably competant non electrical engineer homeowner here. I have a question for the experts: I recently replaced a horrible...
Replies
8
Views
1K
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
911
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
758

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock