Discuss Best way to check if you any faulty appliances ? in the Electrical Appliances Forum area at ElectriciansForums.net

Reaction score
0
Our electric bill has double within the last 6 months and the electric company are now saying the bill will be £440 a month. The electric company installed a check meter to see if the main meter was faulty. The readings comeback fine and they are now saying that it is down to our usage. We live in a 3 bed house my wife is at work all day and I'm still working from home (using a laptop) and my stepson goes to work every afternoon. We have a made a point to keep electric use down to a minimum but the readings are still increasing. What is the best way to check if we have any faulty appliances or does any one know of a company that would come and investigate ?
 
£440 a month would supply a medium size cannabis farm. something isn't right unless you are using a lot of heating appliances. no appliance can draw more than it's rated current, so I'd be looking for an illegal tap off to next door as one possibility. check attic.

just for info, we are in a 4 bed semi. occupied mostly all dayand our monthly leccy is about £80-£90
 
Take a reading from the electric meter several times in the day, morning, lunch early evening and last thing at night.
Compare the usage between each reading and narrow down when the highest usage is.
You may need to do it for a few days to compare days as well.
 
Are your suppliers suggesting £440/mth to 'get back on track'?

£440 sounds a lot but if it is partly for previously used units it presumably would be short term?

Many people have found their usage has increased working from home these past 18 months or so and whilst a laptop uses very little power, extra teas and coffees, heating, lighting all add to it.
Has the unit rate changed (£/kWh)?
Has an immersion heater been left on 24/7 or thermostat not working correctly?
Have you had an electric vehicle charger installed in last 6months or so?
 

Reply to Best way to check if you any faulty appliances ? in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
422
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
407
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
288
Does anyone else get emails and phone calls from companies and agencies say we seen your CV and we want you to apply for our job. And when you...
Replies
4
Views
606

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock