Discuss blanket testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Hi Mich.

Basically you are testing the whole of the istallation in one go by testing on the supply tails and MEC.

Obviously you need to take great care when doing this to make sure that you have disconnected all electronic devices from all circuts lamps out neons in spurs disconnected with all loads connected in. Testing of 2way switches in both positions so as to test strappers aswell.

If the combined I/R is less than 2MO then you need to test each circuit individually to find the low reading one and investigate further.
 
I'm as above, but for pir, I have a lead that looks like a small jump lead.
2 very strong and large cocodile clips, insulated, , and 1 meter of white flex.
With the main switch off, and all cpd on.
On IR testing, I connect the lead to N bus and L bus. test L/N to earth.
I also use this to test eli by taking the croc, off the N bus and connect to the E bus.
 

Reply to blanket testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
587
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you should...
Replies
0
Views
499
Hi All DALI lighting system distributes circuit via LCM's, for electrical test, do you stop at the LCM or light point. how do you carry out...
Replies
2
Views
392
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you...
Replies
0
Views
446
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock