Hello all

Just some input needed

I have 16mm meter tails & earth looks undersized coming unto the board also. I want the consumer unit changed, I understand that the tails need to be 25mm & earth 10mm I spoke with my electricity supplier who is going to get the technical department to call next Friday about changing these. Seems like it's going to take a while.

Can I get the board changed with the existing set up first, new rcbo board installed on the 16mm tails & current earth, then after upgrade the meter tails?
 
I'd love to know how they calculated that, 16mm tails are fine on a 80a fuse also. Is the board located beside the meter or further away?
 
I'd love to know how they calculated that, 16mm tails are fine on a 80a fuse also. Is the board located beside the meter or further away?
The board is just behind the meter. So I don't need to wait for any tail or earth upgrade. Its ok to go ahead with the 16mm tails, I think the tails to the Meter from the consumer will be changed anyway by the electrician. It'll just be the 16mm coming from the fuse to the meter which be 16mm. I'll get on this now o know I don't have to wait
 
they wont put 100A fuse in unless 25mm tails. As for the upgrade I'd check your bonding if you say has small earthing conductor.
 
If it is, or soon will be, on a PME system (i.e. TN-C-S) then 10mm is the minimum extraneous bond size (Table 54.8) , and obviously that also applies to any incoming earth...

Also from the simple guide (Table 54.7, not adiabatic computation) for CPC size then for 16mm tails your main earth should also be 16mm, as it would be for 25mm tails.

For an existing installation without signs of thermal stress then often you would simply let it be, but if you are looking for a supply upgrade to 80A or 100A then it makes sense to check and impose the current regulations of cable sizing.
 
Hello all

Just some input needed

I have 16mm meter tails & earth looks undersized coming unto the board also. I want the consumer unit changed, I understand that the tails need to be 25mm & earth 10mm I spoke with my electricity supplier who is going to get the technical department to call next Friday about changing these. Seems like it's going to take a while.

Can I get the board changed with the existing set up first, new rcbo board installed on the 16mm tails & current earth, then after upgrade the meter tails?
Yes, it's fine to get the board changed now. The best option would be to get a Henley block installed with the existing 16mm tails from the meter going in, then 25mm tails to the new board. That way, if you get the fuse upgraded the DNO/meter supplier can easily change their tails with no inconvenience to the existing installation...

Note you may need to get the meter tails changed separately by your electrical supplier - they own the meter, and the DNO look after the main head (in some areas they will liaise, but in others you may need to get both involved...)

Whoever you get to install the board should be able to give guidance on earth sizing and whether any upgrade to existing bonding will be needed.
 
I would class 16mm tails as acceptable with a 100A fuse if max demand is not going to exceed the current carrying capacity of a 16mm conductor, also it would have to meet regulation 434.5.2. I.e Any fault occurring shall be interrupted before the permitted limiting temperature of the conductor is reached. You calculate this by using the given equation within the regulation.

The above advice can be seen in Best practise Guide 6, point 6.1 note 4.
 

Attachments

  • 6.Consumer unit replacement in domestic and similar premises.ESC Best Practice Guide No.6.pdf
    935.1 KB · Views: 17
The above advice can be seen in Best practise Guide 6, point 6.1 note 4.
Just to note this is now Best Practice Guide 1 (Issue 4) Point 5.1, Note 4.

BPG 1 Replacing a consumer unit in domestic premises.

BPG 6 is now portable and stationary appliance testing in private rented accommodation.

Up to date BPG’s here.
 
I would class 16mm tails as acceptable with a 100A fuse if max demand is not going to exceed the current carrying capacity of a 16mm conductor
Certainly for tails in open air. While they stop at 25mm for that case, a look at Table 4D1A columns 11 & 12 shows 25mm rated at 130-146A and scaling that by the sort of ratios seen for, say, clipped direct (column 6) gives ratings of at least 100A for 16mm.

But often DNOs complain if it is not 25mm so if installing new than it is easier to go with that. If you use the Doncaster easy-fit 19-standed version they are not too difficult to wrangle.
 
Yes, it's fine to get the board changed now. The best option would be to get a Henley block installed with the existing 16mm tails from the meter going in, then 25mm tails to the new board. That way, if you get the fuse upgraded the DNO/meter supplier can easily change their tails with no inconvenience to the existing installation...

Note you may need to get the meter tails changed separately by your electrical supplier - they own the meter, and the DNO look after the main head (in some areas they will liaise, but in others you may need to get both involved...)

Whoever you get to install the board should be able to give guidance on earth sizing and whether any upgrade to existing bonding will be needed.
Just had the electrician in and the incoming earth is 6mm so he wont change the board until the earth is upgraded. the bonding is also 6mm
 

Reply to Board change on 16mm tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock