Yes, it's fine to get the board changed now. The best option would be to get a Henley block installed with the existing 16mm tails from the meter going in, then 25mm tails to the new board. That way, if you get the fuse upgraded the DNO/meter supplier can easily change their tails with no inconvenience to the existing installation...Hello all
Just some input needed
I have 16mm meter tails & earth looks undersized coming unto the board also. I want the consumer unit changed, I understand that the tails need to be 25mm & earth 10mm I spoke with my electricity supplier who is going to get the technical department to call next Friday about changing these. Seems like it's going to take a while.
Can I get the board changed with the existing set up first, new rcbo board installed on the 16mm tails & current earth, then after upgrade the meter tails?
Note you may need to get the meter tails changed separately by your electrical supplier - they own the meter, and the DNO look after the main head (in some areas they will liaise, but in others you may need to get both involved...)
Whoever you get to install the board should be able to give guidance on earth sizing and whether any upgrade to existing bonding will be needed.