Discuss Board Change Questions in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
17
So im looking to get certified with Stroma, signed up and my first job that I can use for the assessment is a board change.

The only issue is it doesn't have bonding to the main water. Can I change the board and put the fact there is no bonding down under as an advisory?

Thanks for your help in advanced
 
So im looking to get certified with Stroma, signed up and my first job that I can use for the assessment is a board change.

The only issue is it doesn't have bonding to the main water. Can I change the board and put the fact there is no bonding down under as an advisory?

Thanks for your help in advanced

No. Bonding needs to be included as part of the CU change.

I wouldn't recommend your approach unless you want to fail your assessment.
 
Lack of bonding is a C2 on an EICR/PIR. Do you really think that it is acceptable to leave it (regardless if it's for your scam membership or not ( unless you're a sparky near me that charged 2 days for an 8 way board change and left the bonding)! :)
 
So im looking to get certified with Stroma, signed up and my first job that I can use for the assessment is a board change.

The only issue is it doesn't have bonding to the main water. Can I change the board and put the fact there is no bonding down under as an advisory?

Thanks for your help in advanced

Hmmm, And exactly what electrical qualifications do you hold??
 
Bonding to the Gas, water etc is part and partial of a board change, if it's already in place, and continuity tests OK 0.05ohms is the limit, correct size cable used 10mm, I did read a recommendation somewhere that if the run to each of the items that require bonding is over 25mtr then you must increase the size of main bonding conductor. In answer to your question. no you cant leave an advisory.
 
sorry, pete. that 0.05 ohms is the max. you should get between the bonding conductor and the pipe it's connected to, not the resistance of the conductor itself.
 
Hmmm, And exactly what electrical qualifications do you hold??

2330 Level 3
NVQ L3
AM2
2394
2395
17th Edition

Any more questions before you answer my simple question?


Only asking because one of the lads at work says its what he does, it will be a nightmare to get a cable through to the other side of the house.

Thanks for all the decent/non-derogative reply's so far!
 
i disagree. if you can quote the reg. that proves me wrong, i'll eat the pie.
 
It will be a nightmare as its at the other end of the house. It will be a difficult job to make it look tidy.

It would also mean taking up the flooring in all rooms upstairs.

Do a search or 2 on here. Remember the location of the bond needs to be within 600mm of entry to the premises "where practical".

I would question your "mates" about their claims - because I can't imagine they are compliant on their installs, regs nor certs.
 
Unfortunately if it's got to be done it's got to be done , I had one about month ago right to the other side ofthe house but it had to be done
 
2330 Level 3
NVQ L3
AM2
2394
2395
17th Edition

Any more questions before you answer my simple question?


Only asking because one of the lads at work says its what he does, it will be a nightmare to get a cable through to the other side of the house.

Thanks for all the decent/non-derogative reply's so far!

Sorry but you should know better as you seem adequately qualified so to speak, I'm not trying to sound rude but how can you possibly not know this? I'm disgusted that you would even consider leaving it off.

If your mate leaves it off then he is a fool and going the extra mile to wrecking this industry!
 
Do a search or 2 on here. Remember the location of the bond needs to be within 600mm of entry to the premises "where practical".

I would question your "mates" about their claims - because I can't imagine they are compliant on their installs, regs nor certs.

Unfortunately it goes from the outside path under the house to under the sink.

His reason is because hes not adding or altering the existing install He's changing the board to make it safer.
 
so by the same reasoning, he's fit a new c/h boiler but leave the gas leak on the gas fire leaking?
 
Unfortunately it goes from the outside path under the house to under the sink.

His reason is because hes not adding or altering the existing install He's changing the board to make it safer.

There is always a way to do it, it's pure laziness in my opinion. Making bit safer yes, but with no regard to the regs. If he can't be asked to do do a simple task like bond the water, I dread to think how good the board change is...
 

Reply to Board Change Questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
819
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
274
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
692
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock