Discuss Boiler/Generator problem in the Industrial Electricians' Talk area at ElectriciansForums.net

J

jude

Hi
I’m trying to run a gas combi boiler from a 2500kva petrol generator, but the boiler shuts down when connected to the generator displaying a supply problem.
In the boiler house I have 2 separate sockets one coupled to the domestic supply the other one a direct feed from the generator, the idea being that if there was a domestic power failure, I would just unplug the boiler from the domestic supply and plug it into the socket fed from the generator.
I’m able to run everything else I have tried from the generator i.e. power tools, lights etc just not the boiler.
Any help would be much appreciated.
Thank you
 
What test equipment do you have?

Most likely the generator does not have a voltage regulator built in, or if it does, it's not working properly.
Or, the engine is running at an incorrect speed giving you an incorrect supply frequency.

Compare the brightness of a filament lamp on normal mains and the generator if you have no test equipment.

Also, try loading up the generator in the range of 500-1000VA (maybe a fan heater on low heat setting) and see what the boiler does when the additional loading is present.

Simon.
 
Are you using a generator that gives a true sine wave output or is it an inverter type generator, As previously stated frequency could be an issue I have heard of a number of new generators recently with outputs in excess of 65Hz with no load and the frequency only getting down close to the 50Hz with about 70% of full load output connected
 

Reply to Boiler/Generator problem in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

As a young man, I was an electrician, but now I'm getting on, I am strictly DIY. I used to have a cheap old 900W petrol generator connected to a...
Replies
8
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
548
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock